Replacing my hob and found this. Hob (6.4kW) installed on a dedicated 32A circuit, wired with 6mm TE. Five terminals on the hob, two lives and two neutrals have each been bridged with 1.5mm wire. TE cable is wired to one of the lives and one of the neutrals. Is this correct? Thank you
 
the bridging links are usually flat brass links, fitted by manufacturer. should not be wire. check manual for wiring diagram/s. your fixed wiring supply is correct.

as always. a photo would help.
 
Thank you telectrix for your reply.

Weirdly my new hob didn't come with the brass links
Hopefully you can see the image attached

The hob as new is supplied with 5 core 1.5mm cable

Thank you again.
 

Attachments

  • IMG20210814165426.jpg
    309.5 KB · Views: 50
Put the flex back on it, the crimp lugs have not been terminated properly, looks like plier marks not crimp indentations

the cable is not heat resistant, it probably should be but a check in the manual should confirm.
 
I would rather rely on factory crimps on the 5 core 1.5mm flex originally supplied by the manufacturer (with one tag on each terminal, and then appropriately joined remotely), than DIY crimps on 6mm solid conductor cable.

The links in the photo seem to have a factory crimp one end, and a DIY crimp the other, showing the same sort of marks that James mentions above. Could they be made from the flex?

It's most important to use a good quality ratchet crimp tool to make such joints, especially on solid conductors.
 
Agree with everything above.
if the power was turned off and the cable tugged a little, I would bet the cable comes out of the crimp with ease.
 
Probably a quick job for a sparky with the correct tools and parts in the van.

I would not suggest a DIY repair on this.
 
As above, the crimps on the 6mm twin and earth are dangerous and should be removed. Someone has also used the incorrect crimp for the 2.5mm cpc, it should be blue.
A good quality ratchet crimper needs to be used otherwise the joints will heat up and eventually fail. Worst case scenario is a fire.
 
As above, unsiatisfactory crrimping with unsuitable tools and connectors that will likely result in overheating, maybe not now while the copper is clean and bright but in a year or two once it has oxidised. A properly made crimp needs not only to be mechanically attached, but to make a gas-tight cold-weld between cable and terminal.
 
Look inside the terminal block of your new Hob, you may find the brass links already there, but as others have said, should really be heat proof flex, especially if the hob is above an oven with a cover plate between the two with reflective foil.
 
Is the photo your new hob or old one?

the new one should have all the bits needed, including a length of appropriate flex, with crimped ends, and any copper links. (Check they’re not in a bag with fixing brackets)

If in doubt, RTFM
 
Thank you all very much for your replies.

So other than the poor crimping on the ferrules, and the lack of heat resistance, the actual wiring is correct?

Thank you again,
There are no other parts of the actual wiring.

what you should have is a switch above the worktop to turn it on and off.
an appliance outlet at the back of the cupboard space to wire the flex from the hob to.
a suitable specified flex (NOT TWIN AND EARTH) between the wall and the hob
correct termination of all conductors and good quality workmanship throughout.

From what you have shown us, ABSOLUTELY NONE OF THAT HAS BEEN ACHIEVED.
 
That 5 core flex needs to go back on and any linking done at the end of the flex not attached to the hob. The 6.0mm cable will be putting enormous strain on those PCB terminals.
 
If the hob did indeed come with 5-core 1.5mm2 flex, intended to be used on a 3-phase supply, but the hob is now to be used on a single phase supply, I'm thinking the N is now not going to be adequately rated at full load? Unless there is built-in limiting of the max current on single phase operation (which there might be).
 
In the first message it was stated that the photo is of the existing hob, and they have bought a new one to replace it.

Would the OP confirm that the photo is not their handiwork.


if the new hob comes with 5 core flex, then links may not be required. Each core will have its own terminal, and the doubling up will be done at the wall outlet.
 

Reply to Hob wiring question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
927
Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
Replies
23
Views
4K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock