What size supply would you install for a kind of wendy house in the garden that's going to be used as an office for 2 or 3 people.

around 6 sockets and a double fluorescent. They'l probably be plugging in a 2kw heater at some point when it gets to winter.

Is a 32A feed on 4mm swa a bit overkill? Knock it down to a 2.5mm on a 20A? what would you do? probably not much cost difference.

Was planning on running a 16A radial socket circuit and a 6A radial for light.

Thanks
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
So many variables jack....
Firstly, are you an electrician?
Secondly, this is notifiable work, so are you part P registered or are you informing LBC?
 
  • Thread Starter Thread Starter
  • #3
Yea this is LEGIT. Part p registered. I'm more of a commercial industrial electrician though.
 
Yea this is LEGIT. Part p registered. I'm more of a commercial industrial electrician though.
Good stuff.
I have found that most "home offices" actually get by quite nicely on a 13 amp supply, even with a fan heater and a couple of computers, but only you can know what the loading is likely to be.
We need to know the length of run first of all mate, to calculate volt drop, along with ccc.
 
  • Thread Starter Thread Starter
  • #5
Yea the runs about 20M, swa clipped direct and then buried in the ground.

I'm thinking there's probably going to be about 3 computers, and other general office stationary printer, photocopier etc then a 2kw heater.
 
E

Edd

For what its worth theres nothing like running a supply then finding out its too small latter, for the lil extra cost go with a 32-40 Amp supply. You may find it really cold in the winter and need more heaters. look into what earthing system your gona use. TT the office, or export the house earth..
 
Yea the runs about 20M, swa clipped direct and then buried in the ground.

I'm thinking there's probably going to be about 3 computers, and other general office stationary printer, photocopier etc then a 2kw heater.
In this situation, I'd probably be inclined to agree with Edd. 32A supply.
Any metalwork entering the office (pipework/steelwork etc.) ?
 
  • Thread Starter Thread Starter
  • #8
No metal work in the office, so was planning on running a 3 core and export the tn-c-s.
 
Sounds like a plan.
So, as you will be using lighting in there, work out what size cable you will need for your 20M run, to allow for 32A supply with no more than a 3% vd.
 
  • Thread Starter Thread Starter
  • #10
ah yea it would have to be a 6mm for a 32A supply to be under 6.9v. i'l re measure the run perhaps i was being a bit generous, it might be more like 15M.
 
Also Jack I would take a bit of CAT cable out and telephone cable foe data and telephones.........................after all you only want to dig that trench once
 
Or a wireless 'N' router ;)

It's people like you that are trying to take the food out of our bairns mouth ............there we are hard working leccy's trying to earn a honest crust and recommend earning a few pennies by installing some data/telephone cable and your suggesting wireless ..................I don't know









:teeth_smile::teeth_smile:
 
T

Tidy Max

You can't beat a wired internet connection, even if the internet connection is good there is not garunteeing the wireless transmitter in the router is decent. Virgin Superhub comes to mind!

Sent from my GT-I9300 using Tapatalk 2
 
It's people like you that are trying to take the food out of our bairns mouth ............there we are hard working leccy's trying to earn a honest crust and recommend earning a few pennies by installing some data/telephone cable and your suggesting wireless ..................I don't know









:teeth_smile::teeth_smile:
Ha ha, just testing the water! In truth, I'd be running a telephone/data cable and a Sky+ feed if it was my home 'office' ;)
 

Taylortwocities

-
Arms
Esteemed
ah yea it would have to be a 6mm for a 32A supply to be under 6.9v. i'l re measure the run perhaps i was being a bit generous, it might be more like 15M.
Don't forget that your total distance is measured from the intake, not the hole in the wall where the cables comes out into God's fresh air.

6mm 3 core IMO. That will mean you can boil a kettle and have the heating on at the same time!
 