I have done some work for a security company . There is nobody at the office this week who can help me solve the following problem I am having, so I thought I would try this forum.
I am trying to get a light to switch on only when it is dark (a light sensor is open) and a gate sensor is activated.
I am using links to link a RIO (1051) zone to an output. The way I have configured it is as follows.
LINKS
001 1051 -> LINK A, group, A1
Photocell sensor: Zone
1051 set log, group A1
Relay to lamp: Output
1051 -> LINK A, pulse 120 seconds, group A1
So I have the light switching on for 2 minutes when the photocell is activated.
I have a relay wired into zone 1015 on the Galaxy board, which is switched by a light sensor. I am getting 1k ohms during the day and 2k ohms at night.
My question is, can I use LINKS so that the relay switching the light is only activated when zones 1051 AND 1015 are open (2k ohms)