A

agouldm9590

I am being asked too install a local fuseboard within an outbuilding containing a hot tub, the proposed location for the fuseboard is about 1.4 metres from the edge of the hot tub and about 2 metres off the ground. Does this need any sort of enclosure surrounding it or is IPx4 sufficient enough, also with regards too general lighting does it need too be low voltage? Am I right in applying the special location as a swimming pool OR other basin. Please get me back too me with your thoughts! Thanks!
 
Providing your hot tub is freestanding ( i.e. not constructed below ground level like a swimming pool) it can be treated as a normal bath tub under BS7671:2008, Amt 1, Section 701. Your proposed location for 'fuseboard' whilst no ideal, would be outside the zones so the general BS7671 regulations effecting environmental conditions and IP ratings apply. 30mA RCD additional protection is required for all low voltage circuits within the location 701.411.3.3. If your lighting is located outside the zones (i.e. >2.25m from finished floor level) the normal low voltage supply can be used. You will also need to consider the route, installation method and possible mechanical protection (or additional protection) of your sub-main to the 'fuseboard'. Consideration of your disabled person (particularly if wheelchair bound or infirm) should be given to the access to the tub, the height and location of all accessories, including the 'fuseboard' which at 2m from the finished floor maybe otherwise inaccessible. Guidance is given in Part M of the building regulations where it is suggested that all accessories and controls are located between 0.45 - 1.2m from the finished floor level.
 
Last edited by a moderator:
Thats been a great help, erased any uncertainty now as this is a new location for myself, the problem I have is that the owner has pulled in all cables etc himself so I am trying too work with what I have, thanks again, top man!
 
If the customer has installed all the cabling for this outhouse, then you will need to check if this is fed from a PME installation?? If it is a PME supply then you must have a 10mm bonding conductor back to the main installations MET, connecting to any metallic services such as the water supply pipe, supplying this hot tub installation...
 
If the customer has installed all the cabling for this outhouse, then you will need to check if this is fed from a PME installation?? If it is a PME supply then you must have a 10mm bonding conductor back to the main installations MET, connecting to any metallic services such as the water supply pipe, supplying this hot tub installation...

The idea is that the 6mm SWA the customer has pulled in is be connected too the original consumer unit, tagging down the sheath and 3rd core being used as a spare earth too that end of the installation, so thus the SWA itself is protected by the rcd that end, then at the other end is too install a 'Garage RCD Board' and supply it using two remaining cores from the 6mm SWA, from this I plan too install a spike into the ground and run a 16mm from the spike too the 'Garage Board', I am pretty sure that the hot tub doesnt have any sort of cold water supply coming into it, its purely filled up via a hose, therefore a Water Bond will not be necessary. What are your thoughts? Thanks.
 
Is it a PME or TN-S supply into the main supply?? And if TN-S, why are you dropping that earth in favour of a TT earth?? Come to that, why are you dropping the PME/TNC-S earth in favour of a TT earth, ....this installation is in essence, going to be no different than the bathroom in the main house when all said and done??

Why are you putting 2 X 30mA RCDs in series?? I think you'll find, that ...the hot tub's electrical installation will also incorporate RCD protection. You may find, you'll have multiple RCDs in series from what you have stated above.

Think you need to read the manufactures data sheets on this hot tub, and find out for certain if there is going to be a permanent water supply or not to this unit...
 

Reply to Hot tub for disabled adult - queries on zoning and ratings. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have my tin hat on because I know this has been done to death and have read through a lot of the old posts. I just wanted to run my proposal...
Replies
58
Views
7K
Like I said, don't just give it up, choose what you want to do, and do no more...or words to that effect! I'm back on my Men's Shed charity thing...
Replies
9
Views
2K
E
Hi all, I have had a QUICK look in the regs book and it seems that kitchens are not covered under the special locations and zoned locations. At...
Replies
11
Views
16K
T
J
NICEIC Certification Scheme NICEIC view on PME for an outside hot tub?
Hi everybody I'm new to the forum. I need some help with a small problem concerning PME. I'm putting in a supply to a 32A commando socket...
Replies
3
Views
8K
andekoch
A
U
Am installing a hot tub and the electrics have already been installed. 32Amp, RCD protected, run in 6mm SWA. Problem is this terminates in an...
Replies
3
Views
2K
PC Electrics
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock