Hi all im looking for some advice on installing a hot tub, the supplier specifies a 16 amp type c mcb, a 20 amp rotary switch and an ip rated 13 amp socket with rcd protection, the run of swa cable from the consumer unit to the rotary switch is 30m, I will then run an swa from the rotary switch to the ip rated 13amp socket for the hot tub to be plugged in direct, what im needing advice on is the voltage drop, the cable will be clipped direct to a wall, 30m run, ive worked it out that there will be a voltage drop of 10.5v which works out at a vd of 4.6%, do yiu agree that a 2.5mm swa cable will be more tham man enough to run the hot tub, cheers.
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
Hi the hot tub only draws 13amps as its a plug and play,
Hi the hot tub only draws 13amps its a plug and play cheers
[automerge]1593455281[/automerge]
Hi Ive worked out the voltage drop to be 7.41 volts, mV/a/m x Amp x Metre /1000 = 19 x 13a x 30meters /1000 = 7.41 vd
Reply to hot tub installation in the UK Electrical Forum area at ElectriciansForums.net
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Hi, looking for some advice, 6mm swa allready installed to a hot tub Client now wants additions and my calcs say the original swa is allready too...
Upgrading the Hot Tub to a Swim Spa, current power for the hot tub is 6mm 3x core swa to a 40amp mcb and 40amp rotary isolator. Cable is clipped...