Hotel extension built 1989 multiple boards each serves 2 rooms,heat, light, sockets, telemetry controled heating from reception, parent board supplies sub via 4mm SWA on a 32A type 2.Sockets 20A b curve, heating 10A b lights, 10A b, sockets are ring final in 2.5/1.5 It's my understanding that has been done like this to get the Zs down otherwise it would be out with the required disconnection times, I do not have any real concerns over this, but, is this a normal approach, I would have uped the cable and supply breaker and ultimately the RF to 32A there are 36 rooms done this way so maybe cost was an factor when the job was quoted who knows any thoughts
Pict
 
So one 20A ring supplies two rooms?

If heating is taken care of then the largest ring load will probably be 2 hairdryers running concurrently for a short time plus a bit of background for televisions etc.

Sounds fine, of course if Zs is a problem and you want to 'upgrade' you could swap the 20A MCB's for 32A RCBO's, bearing in mind that your distribution circuit is only at 32A too!
 
Sorry, no its one board two rooms one set of breakers per room 20,10 and a 6 didn't describe it to well !! each room has as you say a telly kettle hairdryer and a coffee perker cant think of any thing heavier a guest may bring with them, but then again??
Pict
 
Could be a consideration to assist with discrimination downstream, to protect the sub main from isolating?

Or it could be that the deSign was switched to 20Amp to allow for a smaller size sub main.
 
Last edited:

Reply to hotel pir in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all! Posted on here a couple of years ago and got great advice. Have been self employed a couple of years now and always find pricing work the...
Replies
10
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hi I've got a job that i've been asked to quote for and i'm struggling with how to do it the best way. It's a summerhouse and the customer only...
Replies
17
Views
3K
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock