Called to a house where customer's were getting electric shocks from their dishwasher and radio in the kitchen.
Went through the usual steps l, assuming it was an absence of CPC and a bit of earth leakage from the appliances.
After a few frustrating hours pulled this beauty out of the kitchen ceiling. Somehow the nail had disconnected the earth going back to the MET and then bridged line and the CPC on the rest of the radial , all without tripping the MCB or RCD.
Went through the usual steps l, assuming it was an absence of CPC and a bit of earth leakage from the appliances.
After a few frustrating hours pulled this beauty out of the kitchen ceiling. Somehow the nail had disconnected the earth going back to the MET and then bridged line and the CPC on the rest of the radial , all without tripping the MCB or RCD.