Hi everyone,

How do you choose Rccb Rated Current at the your country?

Do you have an official document about it?

What do you reference for nominal current coordination with mcb before it?

How to calculate the rcd rated current and mcb rated current coordination, is there a document about it?

Thank you from now.
 
If you are talking about the current carrying capacity of the device, yes it would be coordinated to be capable of handling the expected load current.

If you are talking about the tripping current, we typically use 30mA for additional protection (i.e. protection of the end user of the installation) and the protection of sockets rated at 32A or less, 100mA for sockets rated at >32A and for providing selectivity in some cases such as protection the internals of metal consumer units when the earthing system is TT and not exceeding 300mA for protection against fire.

I'm sure someone will correct me if I'm wrong :)
 
If you are talking about the current carrying capacity of the device, yes it would be coordinated to be capable of handling the expected load current.

If you are talking about the tripping current, we typically use 30mA for additional protection (i.e. protection of the end user of the installation) and the protection of sockets rated at 32A or less, 100mA for sockets rated at >32A and for providing selectivity in some cases such as protection the internals of metal consumer units when the earthing system is TT and not exceeding 300mA for protection against fire.

I'm sure someone will correct me if I'm wrong :)
I know it, thanks, but Is there a formal calculation or figure that I can refer to for selecting the rated current, more about the selection of rated current that I want to learn? :)
 
The RCCBs rated current carrying capacity should simply be large enough to handle the expected load. How you calculate that will depend on what it's supplying.

In domestic, the regulations suggest that RCDs should have upfront over current protection, so in a lot of our consumer units that means if the main service fuse is rated at 60A, the RCDs should be rated at 63A, if it's an 80A fuse, the RCDs should be able to handle 80A. Some suppliers such as Hager provide RCDs rated at 100A since this is the largest standard service fuse size in domestic installations.

Previously we would size the RCD for the expected load it was going to handle using diversity. You can find out about diversity and how it applies to sizing protective devices by doing a search on YouTube for SparkyNinja and Diversity. He's done a webinar recently about it and uploaded it to YouTube.
 
If you are talking about the current carrying capacity of the device, yes it would be coordinated to be capable of handling the expected load current.

If you are talking about the tripping current, we typically use 30mA for additional protection (i.e. protection of the end user of the installation) and the protection of sockets rated at 32A or less, 100mA for sockets rated at >32A and for providing selectivity in some cases such as protection the internals of metal consumer units when the earthing system is TT and not exceeding 300mA for protection against fire.

I'm sure someone will correct me if I'm wrong :)
i wouldn't dare. ;)
 
Yes... if the MCB has a tripping current of 32A, then if the RCD is after it, it should have a current carrying capacity of at least 32A so that it isn't subjected to a protracted overload.
 
generally the RCD comes before the breaker/s. in a lot of cases, the RCD serves several breakers, so it's current rating needs to be > the total of the breakers it feeds, allowing for diversity of the circuits. so if it feeds 4 x 32A breakers, but with a design load of all 4 being ,say, 75A. you would select a 80A or 100A RCD.
[automerge]1588352262[/automerge]
where have all the avatars gone? mine, sparkchick,s and andy78 are all blank?????
 
So how many amps do you usually use in the main circuit breaker position? How many amps do you choose RCD in such a house?
[automerge]1588352647[/automerge]
Which network system are you using?
[automerge]1588352877[/automerge]
If possible, can you share a sample fuse box image, to better understand amperage?
 
Last edited:
im most houses here, each has a 80A or 100A supply with corresponding main supplier's fuse. the average house will have either a dual RCD dis. board, i.e. a 100A main switch with 2 RCDs, each either 80A or 63A, serving 4-6 circuits each... or each circuit protected by it's own RCDO (RCD and MCB combined.

dual RCD Board:
https://www.NoLinkingToThis/p/briti...d-high-integrity-dual-rcd-consumer-unit/4674g
 

Reply to How do you choose the Rccb Rated Current in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Looking to refresh the MCB and RCCB (100A 30mA) units to my 20 year old Contactum P12/100N CU installed in my house. I have presently a...
Replies
2
Views
260
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
709
How are you calculating maximum demand for the certificate and what should you do if your calculations exceed the main fuse rating?
Replies
9
Views
572
Hello Can anyone confirm for me what the following spec for a Wago TopJob 2202-1201 din rail connector means? The connector can accept max 4mm...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock