Hello all,

First post for me, a very frustrated DIYer whos leaving in a country (Czech Republic) where its near impossible to find an English speaking electrician who knows what they are talking about.

My issue is that the company who installed our vinyl pool a few years back clearly didn't do something correctly with the electrics and the result is that you can get a little shock when touching the pool water and the surrounding deck at the same time. We have already paid for three different 'professionals' to take a look, but all claim it makes no sense.

I've spent hours researching and believe that this is due to equipotential bonding, or lack there of. I'm 100% sure the rebar around the pool was never bonded to any of the other pool equipment.

Firstly, looking for some professional opinions if that makes sense?

Second, looking for some clarification on how to best go about resolving. Important to note, i do not want to do this myself, but after past experience i want to understand it so as to be sure its done properly.

The setup:
In ground pool with a light fixture.
Service pit with all of the equipment is 70cm from the pool
Heat pump is 4m from the pool and obviously connect to the service pit.

What i know is that the heat pump, water pump, and even the water pipes (some lug in them) all have earth wires leading back to the main fuse board. This fuse board leads to another in the garage which finally leads to the main board in the house and all are certified as up to standard.

My idea, and its just an idea, was to chip away the concrete at the four corners to the pool to expose the rebar. No idea then if that can then just run to the heat pump, which is easily accessible, or if it needs to go back to the service pit (headache).

Appreciate you taking the time to read, and even more so for any advice you may have.

Regards,
Steve

P.S If there is an electrician from Czech Republic who's reading and knows what they are talking about, you can have the job :)
 
There is a thread on here with a video that goes in depth on this subject. Haven't a clue where it is but if you want some clarity on the matter this video explains in exquisite detail all about bonding and pools in depth.
 
Swimming pools have all sorts of extra regulations in the UK for the obvious reason that water, electricity, and humans don't make for a happy mix.

I have no idea how systems are normally done in the Czech republic, though it is likely that @Lucien Nunes will. But there are supply arrangements (TN-C, TN-C-S) that might be functioning normally but still have a noticeable voltage between the supply earth and the real Earth.

The two options that you typically have are either:
  • Try to force the ground around the pool and your supply earth to be closer by means of bonding to rebar, buried earth mats, etc
  • Create a local TT supply where there is an earth rod just for the earthing the load(s), and a dedicated RCD to allow any fault in the TT side to disconnect quickly (as the earth rod will almost certainly not divert enough current to take out a fuse or circuit breaker)
Bonding the supply earth to buried concrete reinforcement is quite common practice, in the USA I think it is mandatory in buildings (probably @Megawatt will be able to comment). The issue is the trouble to achieve that after the concrete has been poured & set, and even then to reliably bond you need clamps that will keep good contact and resist corrosion.
 
Last edited:
Here is an example of rebar clamps, no idea where to get price & delivery options for Czech though:
 
Swimming pools have all sorts of extra regulations in the UK for the obvious reason that water, electricity, and humans don't make for a happy mix.

I have no idea how systems are normally done in the Czech republic, though it is likely that @Lucien Nunes will. But there are supply arrangements (TN-C, TN-C-S) that might be functioning normally but still have a noticeable voltage between the supply earth and the real Earth.

The two options that you typically have are either:
  • Try to force the ground around the pool and your supply earth to be closer by means of bonding to rebar, buried earth mats, etc
  • Create a local TT supply where there is an earth rod just for the earthing the load(s), and a dedicated RCD to allow any fault in the TT side to disconnect quickly (as the earth rod will almost certainly not divert enough current to take out a fuse or circuit breaker)
Bonding the supply earth to buried concrete reinforcement is quite common practice, in the USA I think it is mandatory in buildings (probably @Megawatt will be able to comment). The issue is the trouble to achieve that after the concrete has been poured & set, and even then to reliably bond you need clamps that will keep good contact and resist corrosion.

Thanks allot for the info pc, much appreciated.

We had a technician come out to review and make sure that the equipment is correctly earthed etc, and his 'professional' opinion was that the electricity (DC,) is simply being naturally generated.. seems a bit voodoo to me, but I'm obviously not an expert. Based on this however, he claims that bonding is unlikely to work, which is the part i cant wrap my head around. Honestly, it doesn't bother me as much to feel a little tingle, and only ever seem to feel it on broken skin, but I've two kids that its puts off.. moreover, its the uncertainty in my head that something just isn't right and could get dangerous.

If i try to bond the rebar (thanks for the link on clips btw), can i simply run an 8mm copper wire around the edges of the deck connecting at the corners and just one line to the heat pump? Would this accomplish to bond everything together assuming everything in the pit are earthed through the same fuse board.. prepared an expert drawing to illustrate, see attached :D.

Again, appreciate all of the feedback.

Regards,
Steve
 

Attachments

  • PoolSetup.JPG
    32.5 KB · Views: 17
Hello all,

First post for me, a very frustrated DIYer whos leaving in a country (Czech Republic) where its near impossible to find an English speaking electrician who knows what they are talking about.

My issue is that the company who installed our vinyl pool a few years back clearly didn't do something correctly with the electrics and the result is that you can get a little shock when touching the pool water and the surrounding deck at the same time. We have already paid for three different 'professionals' to take a look, but all claim it makes no sense.

I've spent hours researching and believe that this is due to equipotential bonding, or lack there of. I'm 100% sure the rebar around the pool was never bonded to any of the other pool equipment.

Firstly, looking for some professional opinions if that makes sense?

Second, looking for some clarification on how to best go about resolving. Important to note, i do not want to do this myself, but after past experience i want to understand it so as to be sure its done properly.

The setup:
In ground pool with a light fixture.
Service pit with all of the equipment is 70cm from the pool
Heat pump is 4m from the pool and obviously connect to the service pit.

What i know is that the heat pump, water pump, and even the water pipes (some lug in them) all have earth wires leading back to the main fuse board. This fuse board leads to another in the garage which finally leads to the main board in the house and all are certified as up to standard.

My idea, and its just an idea, was to chip away the concrete at the four corners to the pool to expose the rebar. No idea then if that can then just run to the heat pump, which is easily accessible, or if it needs to go back to the service pit (headache).

Appreciate you taking the time to read, and even more so for any advice you may have.

Regards,
Steve

P.S If there is an electrician from Czech Republic who's reading and knows what they are talking about, you can have the job :)
There is no sense cutting up concrete to get to the rebar. Swimming pools are required to have a # 8 bare wire in a ring around your pool. Having said that I’m going to assume the light fixture is 120vac which should be GFCI PROTECTED or RCD as our friends in the UK call it. Get you a hammer drill with a ground rod driver and drill a 1 inch hole through the concrete and then drive a ground rod at each corner. ALL metal parts are required to be bonded and talking about the pump it is required to be GFCI protected also. Good luck my friend
 
There is a thread on here with a video that goes in depth on this subject. Haven't a clue where it is but if you want some clarity on the matter this video explains in exquisite detail all about bonding and pools in depth.

Not sure how to find the thread, but the guy who made that video is Mike Holt. His Youtube channel is a mine of information on this subject, albeit from a US perspective.

I couldn't find the video you were referring to, so tried searching Google. It seems that video has been made private - probably to stop people repeating his experiment.
 
I don't understand why bonding at all four corners is required, all the reinforcing bars in the concrete are connected to each other with tying wire, I would have thought one connection would be sufficient, conveniently in the pit, but then your are reliant on the pool being constructed correctly, if not then even four rods may not do it, but I would try connecting in the pit before going to the expense and work of putting in four rods.
 
Last edited:
My take on this is that you are experiencing results from voltage difference between the pool and its surroundings. This should not exist if all was well. The fact that it exists indicates all is not well. Without knowing exactly what it is I can’t really advise how to fix it, but I do know there is always the possibility that things degenerate and become worse, so I wouldn’t use the pool until you are happy the cause is found and fixed.

Perhaps confirm the light is 12V and is supplied by an isolation transformer?
 
Last edited:
My suspicion is this is a TN-C(S) supply and that the supply earth is seeing several volts of neutral drop, especially if it is rural. However, it might be worse, a TT system without an (functioning) earth rod and the pool is becoming the route for all leakage!

Can the original poster put up some photos of the power supply arrangement and main panel/fuse box so we can guess?

The other thing not mentioned by the OP by raised by @Megawatt is the supply to the pool electrics has to be on a RCD/GFCI. Might as well confirm this while other things are being discussed.

In terms of earth bonding to the concrete then it might well be simpler to just drill and insert some rods at each corner in the USA-style. But as @Mike Johnson says if it has rebar in there, that would be a very good earthing system if attached at any point that can be accessed (assuming without too much difficulty).
 
Not sure how to find the thread, but the guy who made that video is Mike Holt. His Youtube channel is a mine of information on this subject, albeit from a US perspective.

I couldn't find the video you were referring to, so tried searching Google. It seems that video has been made private - probably to stop people repeating his experiment.
watched allot of his vids already, thanks for the tip.
 
My take on this is that you are experiencing results from voltage difference between the pool and its surroundings. This should not exist if all was well. The fact that it exists indicates all is not well. Without knowing exactly what it is I can’t really advise how to fix it, but I do know there is always the possibility that things degenerate and become worse, so I wouldn’t use the pool until you are happy the cause is found and fixed.

Perhaps confirm the light is 12V and is supplied by an isolation transformer?
We actually disconnected the light as the first thing to check and be sure it was not the cause. Issue still there though :(
 
My suspicion is this is a TN-C(S) supply and that the supply earth is seeing several volts of neutral drop, especially if it is rural. However, it might be worse, a TT system without an (functioning) earth rod and the pool is becoming the route for all leakage!

Can the original poster put up some photos of the power supply arrangement and main panel/fuse box so we can guess?

The other thing not mentioned by the OP by raised by @Megawatt is the supply to the pool electrics has to be on a RCD/GFCI. Might as well confirm this while other things are being discussed.

In terms of earth bonding to the concrete then it might well be simpler to just drill and insert some rods at each corner in the USA-style. But as @Mike Johnson says if it has rebar in there, that would be a very good earthing system if attached at any point that can be accessed (assuming without too much difficulty).
Attached some pics of the fuse boards we have. the run is House > Garage > Pool.
How do i check RCD/GFCI? keeping in mind I'm not an electrician :)

About earthing the Rebar.. can this actually do any harm or make things worse? wondering if to just get someone to give it a go and see, but then i'm worried it might make a different issue.
 

Attachments

  • Fuse Boards.png
    1.8 MB · Views: 22
I don't understand why bonding at all four corners is required, all the reinforcing bars in the concrete are connected to each other with tying wire, I would have thought one connection would be sufficient, conveniently in the pit, but then your are reliant on the pool being constructed correctly, if not then even four rods may not do it, but I would try connecting in the pit before going to the expense and work of putting in four rods.
Makes sense, thanks for the feedback Mike.
 
Attached some pics of the fuse boards we have. the run is House > Garage > Pool.
How do i check RCD/GFCI? keeping in mind I'm not an electrician :)
More detailed photos might help!

It looks as if there are RCD at each of the boards, but it is not really possible to say from that level of detail. However, it all looks reasonable quality equipment so I would imagine so.
About earthing the Rebar.. can this actually do any harm or make things worse? wondering if to just get someone to give it a go and see, but then i'm worried it might make a different issue.
Electrically, no.

However, I have no idea of the risk of causing physical damage to the pool arising from trying to access it!

If you are sure there are no buried service pipes or cables around the pool it might be safer to put in rods at the corners beyond the concrete area. Typically rods have to be deep to be effective, say 2-3m, and often they are in 1.2m segments that can be screwed together as they are driven in.

If you are unsure about buried stuff and are willing to dig down manually (and with care in case you do meet something) then by time you have dug a post-sized hole to around 1m down you are probably clear of any buried service cables & pipes.

Here are a couple of UK suppliers of earthing stuff, more from a lightning protection point of view:
 
Incidentally if putting in a ring of conductor around the pool you generally can and should bury is a bit under the surface, less likely to get noticed/stolen and contributes better to the earth conductance. At the corner rods you can have inspection pits to access the wire and rod fixing bolt, etc.
 

Reply to How how to bond existing in ground pool? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
802
Hi, I hope that someone here might be able to put my mind at rest. I have an engineering mind and a reasonable understanding of electical work...
Replies
13
Views
2K
Need some help please. Got a brain teaser for my first post. My pool pump motor cratered over 4th of July. It was working fine and started to...
Replies
13
Views
2K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock