And assuming the supply is 400V line-line.,
 
I (line) = P / V (line) / sqrt(3)
=1000 / 400 / 1.73
=1.45A

By convention we use the line-line voltage in 3-phase calculations (typically 400V in Europe) instead of the line-neutral voltage (typically 230V). But if you want to think of it in relation to an equal size of single-phase load operating on the line-neutral voltage, consider dividing it into three loads of 1/3 the size, taking 1/3 of the current, star-connected between each phase and neutral.
 
I (line) = P / V (line) / sqrt(3)
=1000 / 400 / 1.73
=1.45A

By convention we use the line-line voltage in 3-phase calculations (typically 400V in Europe) instead of the line-neutral voltage (typically 230V). But if you want to think of it in relation to an equal size of single-phase load operating on the line-neutral voltage, consider dividing it into three loads of 1/3 the size, taking 1/3 of the current, star-connected between each phase and neutral.
So kw rating is always the same amount of amps regardless of single or three phase just its split via three phase
 
So kw rating is always the same amount of amps regardless of single or three phase just its split via three phase
No the constants are Load 1kW and 1ph voltage 230v OR
Load 1kW and 3ph voltage 400v
The variable is
The current or 'amps' varies as suggested previously.
 
So kw rating is always the same amount of amps regardless of single or three phase just its split via three phase
The easiest way to look at it is the star-connected case, then you have:
  • single phase = 1000 / 230 = 4.35A
  • three phase = 1000 / (230 * 3) = 1.45A (i.e. single phase / 3)
However, if you have a delta-connected load and no neutral then it is less obvious how a star-connected system might be used for calculations, and results are as @Lucien Nunes just showed. Which is the same.
 

Reply to How many amps are there in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...
Replies
6
Views
361
I will describe my problem in as much detail so you guys might be able to answer my question. I am never home, my Electric bill is $ 28 to $30 a...
Replies
23
Views
1K
when wiring a 240v 50 amp breaker, for example, does each hot wire have to be rated for 50 amps or 25 amps per wire? 100 amp breaker, 50 amps per...
Replies
10
Views
795
Trying to connect a 50 amp inlet box to my Siemens outdoor combination panel 200 amp cutoffs. Can’t figure out where to insert the 50 amp breaker...
Replies
0
Views
4K
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
712

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock