marty1234

anyone know the reg on how mainy cable can go into a circut breaker .
i know on a ring there will be 2 , shower ther will be 1,cooker 1, what about lighting circuits . I was doing some work in a shop and some other spark is fitting new emg lights he is wiring them out off the lighting 6 amp circuit that has 2 1.5 cables in it at present so he is making it 3 .I would wire from the light switch and fit a test key so i did not have 3 cables in the one breaker
some help on this thanks
 
Last edited by a moderator:
As long as its not ALL the lighting on one breaker then i can see no prob.

Common sense would tell you to make sure they are all secure.

Personally i would probably limit to 3 or 4 at a push.
 
anyone know the reg on how mainy cable can go into a circut breaker .
i know on a ring there will be 2 , shower ther will be 1,coocker 1, what about lighting circuits . I was doing some work in a shop and some other spark is fitting new emg lights he is wiring them out off the lighting 6 amp circuit that has 2 1.5 cables in it at present so he is making it 3 .I would wire from the light switch and fit a test key so i did not have 3 cables in the one breaker
some help on this thanks
I would do the same as you.I don't know if there is a particular reg prohibiting it,but to me,a lighting circuit should only have ONE cable at the circuit breaker.If there are more,then surely they should be on a separate circuit with their own CB. I believe that this way you can properly test a circuit,and record results.How do you record results if you have numerous
circuits coming from one CB?
 
thanks mrloy99 you think the same way as me mate . I think 1 cable to each CB for testing the job i would likr to find some sort off reg for this but dont see one . The sparks that are doneing the job seem to think thay are right putting 3 and 4 cables in 1 breaker for there emg lights .Also they are doing fire alarms in the same job so i had i look 5 cables out 1 10 amp breaker 1 for there new fire alarm,2 intruder alarm ,3 central heating,4 roller shutter,5 socket in back shop
I think these guy have to have a think in what they are doing . STILL TO SEE TEST SHEET ON ALL THE 31 JOBS I HAVE LOOKED AT
 
anyone know the reg on how mainy cable can go into a circut breaker .
i know on a ring there will be 2 , shower ther will be 1,coocker 1, what about lighting circuits . I was doing some work in a shop and some other spark is fitting new emg lights he is wiring them out off the lighting 6 amp circuit that has 2 1.5 cables in it at present so he is making it 3 .I would wire from the light switch and fit a test key so i did not have 3 cables in the one breaker
some help on this thanks

hi there

section314

regulation 314.2 is what you are looking for as separate circuits and control, isolation etc

1 breaker 1 circuit as far as i can see end of problem above states that to me

cheers
:)
 
thanks mrloy99 you think the same way as me mate . I think 1 cable to each CB for testing the job i would likr to find some sort off reg for this but dont see one . The sparks that are doneing the job seem to think thay are right putting 3 and 4 cables in 1 breaker for there emg lights .Also they are doing fire alarms in the same job so i had i look 5 cables out 1 10 amp breaker 1 for there new fire alarm,2 intruder alarm ,3 central heating,4 roller shutter,5 socket in back shop
I think these guy have to have a think in what they are doing . STILL TO SEE TEST SHEET ON ALL THE 31 JOBS I HAVE LOOKED AT
that is just crazy s*it.Must be contravening a load of regs there.I know fire alarms HAVE to be on their own.I would imagine,the intruder alarm stuff should be on their own too.Totally separate circuits they all should be on individual mcbs.The 10amp mcb on the sockets is a mite unusual too.Even trying to locate a fault on such a multicircuit must be a nightmare.Have they got rcds on sockets and stuff buried in walls at less than 50mm?
 
Why do you think that more than 1 cable in a breaker is poor practise
If the lighting circuit was both sides of a dist board routing wise then it is safer to feed both sides from the dist board reducing the zs compared with long runs
This is one practical example
There is nothing whatsoever wrong with multiple feeds at one breaker
Circuit design does not have to be as demonstrated in the guides
Safety is the criteria not unusual layouts
 
anyone know the reg on how mainy cable can go into a circut breaker .
i know on a ring there will be 2 , shower ther will be 1,coocker 1, what about lighting circuits . I was doing some work in a shop and some other spark is fitting new emg lights he is wiring them out off the lighting 6 amp circuit that has 2 1.5 cables in it at present so he is making it 3 .I would wire from the light switch and fit a test key so i did not have 3 cables in the one breaker
some help on this thanks

I agree with you on the cooker and shower circuits only one per circuit, but don't forget that a ring main can have more than 2, if a spur is taken off from the consumer unit there would be 3 cables to the mcb.

With the emergency lighting this would need to be taken from the same supply as the lighting for that area, or else it would not illuminate when the supply goes down.

I wouldn't take the supply from the switch. I would take the supply from the nearest light fitting because otherwise you wouldn't have a neutral for the emergency lights.

The total circuit current would need to be calculated and if necessary a new circuit would need to be installed. Because the emergency lighting wouldn't draw very much power, it may well be possible to put them all on the same supply.
 
the new regs state that only one wire is aloud in each mcb. Although it is stupid that as long as you join the cable outside of the CU then it is fine to have multiple circuits!
 
Where in new regs does it say only 1 cable in each MCB? Are you saying we now can't have a spur fed from the ring circuit mcb?
 
Came across this on a pir. Had 2 lighting circuits on one 6a mcb. Checked with niceic for their views and was told its a code 4 'does not comply with bs7671'
 
Why do you think that more than 1 cable in a breaker is poor practise
If the lighting circuit was both sides of a dist board routing wise then it is safer to feed both sides from the dist board reducing the zs compared with long runs
This is one practical example
There is nothing whatsoever wrong with multiple feeds at one breaker
Circuit design does not have to be as demonstrated in the guides
Safety is the criteria not unusual layouts
I believe that this is poor practise because of the inability to acurately test and record results.
Whilst I would agree that your zs can be reduced,by this method,it would take lighting circuits to be in excess of hundreds of meters for your disconnection times to become an issue.
Then there is to question of convenience and fitness of purpose,that requires that disconnection after a fault interupts the faulty circuit only.
I would also record a deviation on a pir.
 
No i dont mean that. I mean that for example in a 6 Amp MCB you can have one 1.0 mm cable for that lighting ciruit and if you have a 32 Amp for a ringmain all you can have is the two ends of the ring in that one mcb.

Understand my madness ?

Sorry if i dont make sense
 
No i dont mean that. I mean that for example in a 6 Amp MCB you can have one 1.0 mm cable for that lighting ciruit and if you have a 32 Amp for a ringmain all you can have is the two ends of the ring in that one mcb.

Understand my madness ?

Sorry if i dont make sense
As previous poster said you can have a spur off the ring connected directly into mcb.
 
As per previous poster....one circuit per mcb, with a spur allowed on the same terminals as a ring circuit. Other than that its one each. with lighting split upstairs/downstairs on two seperate mcbsTheres a one liner in the regs about limiting any single fault to minimise disruption...cant remember the wording exactly, but in order to comply this is the way to go.....
 
I believe that this is poor practise because of the inability to acurately test and record results.
Whilst I would agree that your zs can be reduced,by this method,it would take lighting circuits to be in excess of hundreds of meters for your disconnection times to become an issue.
Then there is to question of convenience and fitness of purpose,that requires that disconnection after a fault interupts the faulty circuit only.
I would also record a deviation on a pir.

434.4
Fault current protection of conductors in parallel

A single protective device may protect conductors in parallel against the effects of fault currents provided that the operating charecteristics of the device results in its effective operation should a fault occur at the most onerous position in one of the parellel conductors

then read 433.1
433.2
regards Des
 
434.4
Fault current protection of conductors in parallel

A single protective device may protect conductors in parallel against the effects of fault currents provided that the operating charecteristics of the device results in its effective operation should a fault occur at the most onerous position in one of the parellel conductors

then read 433.1
433.2
regards Des
Hi Des,sorry,
As I don't have THE book ,I couldn't possably comment on your quoted regs.As you are no doubt aware,BS7671 is not enforceable by law,it is a code of best practice.You asked why I thought it was poor practice and I have given my reply as above. The temptation exists,when testing and verifying,to only test ONE branch of the circuit,especially,when we only have one box to fill in on the test sheet for the multicircuit,the inconvenience also exists in that suitable quidance is not provided.
 
thanks mrloy99 you think the same way as me mate . I think 1 cable to each CB for testing the job i would likr to find some sort off reg for this but dont see one . The sparks that are doneing the job seem to think thay are right putting 3 and 4 cables in 1 breaker for there emg lights .Also they are doing fire alarms in the same job so i had i look 5 cables out 1 10 amp breaker 1 for there new fire alarm,2 intruder alarm ,3 central heating,4 roller shutter,5 socket in back shop
I think these guy have to have a think in what they are doing . STILL TO SEE TEST SHEET ON ALL THE 31 JOBS I HAVE LOOKED AT

I made a post defnding the use of multiple feeds in one breaker with example of a lighting circuit going off from the dist board in opposite directions

I was looking through this thread and read the quote above for the first time (must have not noticed initially)

Just to put my take on things and to be clear to all

Crazy (as described ) seems to be an understatement with regard to the above install
I probably would not hesitate to fail this job on an inspection
eg The fire alarm supply should not be affected by the failure of another circuit

The description above seems to be of get something working with little interest in design or standards

I posted this in case any of you thought that I may be defending this way of installing when in fact the standards I expect to find on a job would seem to be well above what has been described
My thoughts were on a typical single circuit eg a downstairs lighting circuit in a domestic
 
Last edited:
i think one circuit one mcb!i dont think you can feed a radial from the middle of the circuit as this makes it two radials.load is not the problem....its testing ..any r1 r2 will only cover at best half the circuit init...?....not got my copy of 17 yet though so could be wrong
 

Reply to how many cables can you fit in to a circuit breaker in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock