Discuss How Old is Copper Clad Aluminium etc in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Marcus Vaughan

-
Esteemed
Reaction score
240
Hi All,

I'm part way through testing an empty old house with all sorts of older wiring and a 3036 board in order to work out whats needed.

First circuit is copper clad aluminium ring final. I measured one of the strands and have it as 7/036.

Question - am I wrong to assume is imperial?

I do not know when this was commonly used/installed.

In fact I had a decent document or web page once which gave a kind of history of UK wiring with dates etc. - but I can't find it. Has anyone got anything useful?

I need to investigate this particular circuit further as IR for LN = 26 Mohms despite the house being empty, LE and NE at just other 100Mohms so maybe rewiring anyway.

Pictures because we all like pictures, from right to left - circuit 1 is copper clad ring, circuit 2 is copper clad ring mentioned with low IR. Lights are copper - but not sure about the last two yet.

How Old is Copper Clad Aluminium etc 13 Stone Delf CU.JPG - EletriciansForums.net
 

Attachments

  • How Old is Copper Clad Aluminium etc 13 Stone Delf - Distribution.JPG - EletriciansForums.net
    13 Stone Delf - Distribution.JPG
    350.9 KB · Views: 25
I need to investigate this particular circuit further as IR for LN = 26 Mohms despite the house being empty, LE and NE at just other 100Mohms so maybe rewiring anyway.

Not sure why you'd be considering rewiring with an IR of 26 MOhm or 100 MOhm, these are not too bad (for old wiring).
 
From the green sleeving early seventies. Copperclad T&E was normally 1.5 solid or 4.0 stranded. Very few accessories or distribution boards have suitable terminals for the connection of those conductors. Essentially unless they can be terminated correctly it should be rewired.
 
Marcus - I may be wrong but I'm 99% sure the cables you refer to will be imperial sized tinned copper conductors. This type of old cable seems to go on forever in my experience and I'd also suggest the IR readings aren't bad at all ! :)
 
Not sure why you'd be considering rewiring with an IR of 26 MOhm or 100 MOhm, these are not too bad (for old wiring).

Interesting response. I thought it was a bit low. Truth is there are other reasons to rewire anyway, such as not enough sockets and they are all in skirting boards, the floor area for a single ring is a little too big according to guidance as it goes over 3 floors and includes the kitchen, it's an ideal time because the house is empty etc.

But thank you.
 
Marcus - I may be wrong but I'm 99% sure the cables you refer to will be imperial sized tinned copper conductors. This type of old cable seems to go on forever in my experience and I'd also suggest the IR readings aren't bad at all ! :)

OK - another vote for IR not being too bad.
Aluminium is definitely on the inside though, you could scrape the copper of with a knife to see it. Not too easy to get a photo of!
 
Interesting response. I thought it was a bit low. Truth is there are other reasons to rewire anyway, such as not enough sockets and they are all in skirting boards, the floor area for a single ring is a little too big according to guidance as it goes over 3 floors and includes the kitchen, it's an ideal time because the house is empty etc.

Fair enough if there are other reasons. E.g. sometimes when there is only 1 socket per bedroom and you need 3 or 4 per room, it is simpler to start again with a new circuit.
 
From the green sleeving early seventies. Copperclad T&E was normally 1.5 solid or 4.0 stranded. Very few accessories or distribution boards have suitable terminals for the connection of those conductors. Essentially unless they can be terminated correctly it should be rewired.

Thank you. I was thinking early seventies. The adjacent lighting circuits are 1.5/1.0 copper so it seems a strange mix. Partial rewire or what was available at the time. Who knows. I do know that I had a real struggle getting those conductors (neutrals) back into their terminations just because of their size (and quantity).
 
As per Westy probably 4mm² from the early 70s. You would want the 1970 or later metric version of the 14th edition to look up its specs. Agreed that terminations are its downfall. Better than bare ali, because the copper cladding prevents the oxide formation that makes even mechanically sound ali connections go high-resistance, but not as good as copper because it's soft and easily crushed by terminal screws.

There were accessories made specifically for it. MK sockets of the era, for example, with a kind of wide cage-clamp terminal with a flat pressure plate instead of the end of a screw. Will be interesting to know whether these were used in this install.

If you have a mix of 1.0 and 1.5mm² on the lighting, check that the 1.5 isn't copper-clad ali. AFAIK that was the smallest size made, or at least it was necessary to use 1.5 for lighting and 4.0 for RFCs because of its lower conductivity than copper.
 
As per Westy probably 4mm² from the early 70s. You would want the 1970 or later metric version of the 14th edition to look up its specs. Agreed that terminations are its downfall. Better than bare ali, because the copper cladding prevents the oxide formation that makes even mechanically sound ali connections go high-resistance, but not as good as copper because it's soft and easily crushed by terminal screws.

There were accessories made specifically for it. MK sockets of the era, for example, with a kind of wide cage-clamp terminal with a flat pressure plate instead of the end of a screw. Will be interesting to know whether these were used in this install.

If you have a mix of 1.0 and 1.5mm² on the lighting, check that the 1.5 isn't copper-clad ali. AFAIK that was the smallest size made, or at least it was necessary to use 1.5 for lighting and 4.0 for RFCs because of its lower conductivity than copper.

Very Interesting - Thank You. The accessories are all vintage MK but I have not removed any to date. I'll let you know what I find if I get the chance.
 
Silvery/grey outside, pink inside: Tinned copper
Tan/brown outside, silvery inside: Copper clad aluminium
Tan/brown outside, pink inside: Medium rare steak
 
Silvery/grey outside, pink inside: Tinned copper
Tan/brown outside, silvery inside: Copper clad aluminium
Tan/brown outside, pink inside: Medium rare steak

Blimey. I think the house has been wired in medium rare steak.

I'll try and get a slither photo of an offcut. Also apparently an EICR was done prior to selling so I'm trying to get my mits on that.

Thanks all. I'm going to bed.
 
In certain conditions, copper wire must be specially treated to remain effective. Tinned copper wire is a type of copper wire coated in a thin layer of tin to protect the copper from corrosion that would decrease the wire’s efficiency in humid or rainy climates, high-heat environments and in certain types of soil. read MV
 
Hi All,

I'm part way through testing an empty old house with all sorts of older wiring and a 3036 board in order to work out whats needed.

First circuit is copper clad aluminium ring final. I measured one of the strands and have it as 7/036.

Question - am I wrong to assume is imperial?

I do not know when this was commonly used/installed.

In fact I had a decent document or web page once which gave a kind of history of UK wiring with dates etc. - but I can't find it. Has anyone got anything useful?

I need to investigate this particular circuit further as IR for LN = 26 Mohms despite the house being empty, LE and NE at just other 100Mohms so maybe rewiring anyway.

Pictures because we all like pictures, from right to left - circuit 1 is copper clad ring, circuit 2 is copper clad ring mentioned with low IR. Lights are copper - but not sure about the last two yet.

View attachment 50490
CU clad Alum cables were used during the copper shortage 60s 70s if my memory serves me right
 
As already mentioned the solid green earth cable and presence of solid green over sleeving suggests to me 1970s.

Old installations from the 50s and 60s tend not to have earth sleeving and just twisted up bare
 
In certain conditions, copper wire must be specially treated to remain effective. Tinned copper wire is a type of copper wire coated in a thin layer of tin to protect the copper from corrosion that would decrease the wire’s efficiency in humid or rainy climates, high-heat environments and in certain types of soil. read MV

Reddit.
 

Reply to How Old is Copper Clad Aluminium etc in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock