alban moffitt

Regular EF Member
I have run 6mm t and e through the house from the db in the garage on a 32 amp mcb which is rcd protected. the 6 mm cable then goes into the back of an ip66 rated JB on the side of the house. i then intend to run 2 core (live and neutral) 6mm swa up to a workshop using the armour as earth.
my question is do i need to link the armour to the earth in the 6mm cable coming from the db in the garage and if so how do i do this.

On the other end, in the cu in the workshop i have got a 20 a mcb for sockets and 6 a for lights. how do i connect the earth block in the cu to the armour from the swa?
 

DPG

Respected Member
Based on your questions you need an electrician to do this work and also test it afterwards.
 

gazdkw82

Trainee
Trainee Access
I would strongly recommend you get an electrician in to complete your works.

No disrespect, but your questions are basic ones however vitally important for the safety of your installation. Failure to have a broad spectrum of knowledge on the safety aspects of your electrical installation can lead to a simple but fatal error, unbeknown to you once installed.
 

Spoon

Forum Mentor
This work falls under Part P and is notifiable.
 

Matthewd29

Regular EF Member
If this armour isn't correctly glanced your going to end up with a dangerous situation with no earth. If you are unsure how to do this simply do not do it
 

Cid

Regular EF Member
You need swa cable glands. They come with the necessary earthing tag to connect the earth cable. Plenty of tutorials on YouTube on how to terminate swa cables correctly.
 

telectrix

Scouser and Proud of It
Respected Member
any extraneous metal pipes etc. in workshop?????
 

telectrix

Scouser and Proud of It
Respected Member
my post concerned extraneous metalwork, if it's TNC-S system, the you need a 10mm bonding cable back to MET, ot TT the workshop.
 

Andy78

Respected Member
Thanks Cid,
i will use a pirhana nut to connect the armour to the earth
thanks everyone for their input
Will you also be acting on the input to fully test and notify this circuit to building control ? Or are you just choosing to ignore the legal and safety aspects of this job in favour of the input that gets it done to your requirements ?
 
  • Like
Reactions: DPG

alban moffitt

Regular EF Member
Will you also be acting on the input to fully test and notify this circuit to building control ? Or are you just choosing to ignore the legal and safety aspects of this job in favour of the input that gets it done to your requirements ?
 

alban moffitt

Regular EF Member
i appreciate your concern andy78,
of course it will be signed of and notified so rest assured all in good hands. my brother in law is a fully qualified electrician so he is more than capable of doing this
and i work under him ;)
 

Electrician Talk

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.