Welcome to the forum mate.
Please can you expand on what you are planning on doing.
What is the existing earthing system?
Of course, whatever you are going will have to comply with the regs for South Africa.
 
Do they not provide an Earthing terminal MET for you to utilize?
As from the utility poles there's no earth in a feeding cable you only see an earth wire from a prepaid conlog meter which has an RCD and a sp MCB that is used for sub circuits.
You only see the earth from that wire which is going to the plug outlet

Here's an example of what i am talking about, take a look at a picture
 

Attachments

  • IMG_20200609_135332.jpg
    78.5 KB · Views: 36
As from the utility poles there's no earth in a feeding cable you only see an earth wire from a prepaid conlog meter which has an RCD and a sp MCB that is used for sub circuits.
You only see the earth from that wire which is going to the plug outlet

Here's an example of what i am talking about, take a look at a picture
That's no help Mate sorry
 
The existing 3-pin socket should have some sort of earth connection, maybe back via the RCD enclosure to an earth rod. Do you know if that is the case?

Your safest option is to keep the existing RCD but you really need to consider what the maximum load is and how that will be limited in the event of a fault.
[automerge]1591992311[/automerge]
Do you know if the RCD is a RCBO (combined MCB and RCD)?
 
The existing 3-pin socket should have some sort of earth connection, maybe back via the RCD enclosure to an earth rod. Do you know if that is the case?

Your safest option is to keep the existing RCD but you really need to consider what the maximum load is and how that will be limited in the event of a fault.
[automerge]1591992311[/automerge]
Do you know if the RCD is a RCBO (combined MCB and RCD)?
It's RCCB with a Sp Mcb and the Double pole MCB is mainly installed from the outside utility pole
[automerge]1592000150[/automerge]
The existing 3-pin socket should have some sort of earth connection, maybe back via the RCD enclosure to an earth rod. Do you know if that is the case?

Your safest option is to keep the existing RCD but you really need to consider what the maximum load is and how that will be limited in the event of a fault.
[automerge]1591992311[/automerge]
Do you know if the RCD is a RCBO (combined MCB and RCD)?
It's RCCB with a Sp Mcb and the Double pole MCB is mainly installed from the outside utility pole
 
It's RCCB with a Sp Mcb and the Double pole MCB is mainly installed from the outside utility pole
Are you proposing to replace all of this with a distribution board, presumably one with a RCD incomer and then a few MCBs to have more circuits?

In the UK that would not be considered a DIY job by anyone here!

But in terms of your original question, if you have a double pole RCD as the incoming device you can use a rod for the earth in a TT style, though here it would have to be below 200 ohms impedance for 30mA or 100mA incomers, or below 167 ohms for a 300mA incomer.

Typically the use of 100mA or 300mA delay type RCDs would only be in conjunction with RCBOs or similar having 30mA trip for circuits needing additional personnel protection (e.g. socket outlets, lighting where users can poke fingers in to sockets while changing a bulb, etc).

But if your supplier provides an earth as well then generally you should use it.
 
Are you proposing to replace all of this with a distribution board, presumably one with a RCD incomer and then a few MCBs to have more circuits?

In the UK that would not be considered a DIY job by anyone here!

But in terms of your original question, if you have a double pole RCD as the incoming device you can use a rod for the earth in a TT style, though here it would have to be below 200 ohms impedance for 30mA or 100mA incomers, or below 167 ohms for a 300mA incomer.

Typically the use of 100mA or 300mA delay type RCDs would only be in conjunction with RCBOs or similar having 30mA trip for circuits needing additional personnel protection (e.g. socket outlets, lighting where users can poke fingers in to sockets while changing a bulb, etc).

But if your supplier provides an earth as well then generally you should use it.
Finally you got it all right i want to add more sp MCB's so that i'mma be able to sub circuits
 
One obvious question is are you legally allowed to modify that RCB box if it has some sort of electricity supply meter in it?

Another question is what total load are you planning and is the supply rated for that?
 
One obvious question is are you legally allowed to modify that RCB box if it has some sort of electricity supply meter in it?

Another question is what total load are you planning and is the supply rated for that?
It is definitely illegal for me to modify the RCD box, but there would be no problem if i am taking that outgoing wire which is going to the plug outlets and use it as the power feeder to the Breakers that i will use for sub circuits

Lastly, the supply is undoubtedly adequate for the task as i'll be adding few breakers with at least 10 to 20 amps in rating and maybe i'll add only three single pole MCB's
I won't be adding any RCD because i already have the one installed along with a dp MCB
 
That would be a reasonable approach. The only thing to need to be aware of is you will not get any significant selectivity with MCB in series.

For example if the supply MCB is, say, 20A and you fit a 6A light circuit then an overload on the lights (say a couple of time the MCB rating so in the 20-40A range or so) will trip just that MCB, but if you have a fault that exceeds the instantaneous magnetic trip of the 20A MCB (which could be as low as 3*In = 60A here) then by time the 6A MCB has opened to clear the fault the 20A MCB will already be past the trip point and will disconnect as well.

There is little you can do to get round this, but how troublesome it is depends on the fault currents you might see and the impact of a supply breaker trip. For workshops and similar I would normally suggest an emergency light (internal rechargable battery) so it is still partly illuminated and folk can see to get to the board and reset whatever has tripped.
 

Reply to How to install an earthing system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
492
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
265
See attached photo of my new 3 phase supply at my house. Tails supply a Schneider 3ph board. Sparky is in two minds about the correct earthing...
Replies
11
Views
493
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock