How can i wire an earthing system if I am installing a single phase panel board?
Basically what/which type of earthing do you recommend?
Basically what/which type of earthing do you recommend?
Discuss How to install an earthing system in the UK Electrical Forum area at ElectriciansForums.net
What type of supply's are you given by the supplier? TNCS, TNS, TT, PME. In SA?How can i wire an earthing system if I am installing a single phase panel board?
Basically what/which type of earthing do you recommend?
It's mostly the TT supplyWhat type of supply's are you given by the supplier? TNCS, TNS, TT, PME. In SA?
Do they not provide an Earthing terminal MET for you to utilize?It's mostly the TT supply
In some cases they use the TN-C-S
[automerge]1591978251[/automerge]
As from the utility poles there's no earth in a feeding cable you only see an earth wire from a prepaid conlog meter which has an RCD and a sp MCB that is used for sub circuits.Do they not provide an Earthing terminal MET for you to utilize?
That's no help Mate sorryAs from the utility poles there's no earth in a feeding cable you only see an earth wire from a prepaid conlog meter which has an RCD and a sp MCB that is used for sub circuits.
You only see the earth from that wire which is going to the plug outlet
Here's an example of what i am talking about, take a look at a picture
Ok no worries Buddy as long as you've tried to assist, I appreciate thatThat's no help Mate sorry
What exactly are you trying to do Mate?Ok no worries Buddy as long as you've tried to assist, I appreciate that
I want to remove that plug outlet, i have shown you from the picture and install a single phase panel boardWhat exactly are you trying to do Mate?
It's RCCB with a Sp Mcb and the Double pole MCB is mainly installed from the outside utility poleThe existing 3-pin socket should have some sort of earth connection, maybe back via the RCD enclosure to an earth rod. Do you know if that is the case?
Your safest option is to keep the existing RCD but you really need to consider what the maximum load is and how that will be limited in the event of a fault.
[automerge]1591992311[/automerge]
Do you know if the RCD is a RCBO (combined MCB and RCD)?
It's RCCB with a Sp Mcb and the Double pole MCB is mainly installed from the outside utility poleThe existing 3-pin socket should have some sort of earth connection, maybe back via the RCD enclosure to an earth rod. Do you know if that is the case?
Your safest option is to keep the existing RCD but you really need to consider what the maximum load is and how that will be limited in the event of a fault.
[automerge]1591992311[/automerge]
Do you know if the RCD is a RCBO (combined MCB and RCD)?
Are you proposing to replace all of this with a distribution board, presumably one with a RCD incomer and then a few MCBs to have more circuits?It's RCCB with a Sp Mcb and the Double pole MCB is mainly installed from the outside utility pole
Finally you got it all right i want to add more sp MCB's so that i'mma be able to sub circuitsAre you proposing to replace all of this with a distribution board, presumably one with a RCD incomer and then a few MCBs to have more circuits?
In the UK that would not be considered a DIY job by anyone here!
But in terms of your original question, if you have a double pole RCD as the incoming device you can use a rod for the earth in a TT style, though here it would have to be below 200 ohms impedance for 30mA or 100mA incomers, or below 167 ohms for a 300mA incomer.
Typically the use of 100mA or 300mA delay type RCDs would only be in conjunction with RCBOs or similar having 30mA trip for circuits needing additional personnel protection (e.g. socket outlets, lighting where users can poke fingers in to sockets while changing a bulb, etc).
But if your supplier provides an earth as well then generally you should use it.
It is definitely illegal for me to modify the RCD box, but there would be no problem if i am taking that outgoing wire which is going to the plug outlets and use it as the power feeder to the Breakers that i will use for sub circuitsOne obvious question is are you legally allowed to modify that RCB box if it has some sort of electricity supply meter in it?
Another question is what total load are you planning and is the supply rated for that?