Discuss How to properly do an RCD time trip test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
swaRRR
I've seen several videos on these, half of them show an MCB in the 'on' position protected by an RCD also in the 'on' position, earth lead on the earth bar, neutral on the neutral bar, and live on the MCB's line screw terminal.
But then i've seen other videos where the earth bar and the line/neutral terminals on the load/outgoing side of the RCD is used. John Ward for example shows this test with a standalone RCD on a rig board with two pieces of wire coming from line and neutral.
Which one is right?
Which one is right?
Both are right, as long as the live lead is connected to the outgoing side of the RCD the test will work.
If you're testing standard SP RCBO's then the neutral is solid anyway and it won't matter which side of it the neutral is connected.
And if you have an RCD which is downstream of another RCD you can connect the earth lead of the tester to the incoming N to avoid tripping the upstream RCD.
So when they leave a circuit on and test that it's technically not allowed?
In some circumstances it can be useful to see if an RCD is actually working in normal operating conditions too, e.g. that it isn't being blinded by DC leakage. A ramp test can be very helpful under load to see how close it is to tripping "normally"
No point signing off an RCD that works perfectly until you connect any loads!
Thanks for the help mate appreciate it. So i'm right in thinking that for test sheet purposes on an RCD time test we should try to test without a load, for the certs results box?
Reply to How to properly do an RCD time trip test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...