fine as long as the cable feeding the shed does not , in itself, require RCD protection. e.g. SWA.
 
Youd have to create a non RCD protected way, however j doubt anyone will tell you how to do that if you not already aware. Alternatively, install another small board.
 
all depends on if you have a non-RCD weayin the house DB. if so, it's simple.
 
Hi - my preferred method now is to implement the new distribution circuit to the shed with an RCBO as this will provide protection for the whole circuit and shed. You might want to consider a DP iso to dis the outbuilding in the case of a N-E fault on the cable. I see you’re a Trainee, so perhaps ask a Moderator for access to that section if you’ve not already.
 
Hi - my preferred method now is to implement the new distribution circuit to the shed with an RCBO as this will provide protection for the whole circuit and shed. You might want to consider a DP iso to dis the outbuilding in the case of a N-E fault on the cable. I see you’re a Trainee, so perhaps ask a Moderator for access to that section if you’ve not already.
Cheers wilko
 

Reply to how to take supply from split rcd board without rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
646
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
676
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
717
See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
279

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock