Good evening

I am currently a training to become an electrician. I do hold both initial verification and periodic testing qualifications however this is an issue I have never personally had to deal with and was never mentioned on any of my courses as often seems to be the case.

Basically I am wondering how you would hypothetically go about testing either a ring or radial circuit if you didn't have a seperate cpc but the conduit itself acted as this.

Look forward to hopefully getting a response and some clarity

Regards Harry
 
For a radial circuit you can calculate R2. If you measure the continuity of the line and neutral then divide in half this will give you R1 assuming the line and neutral are of the same length. Then measure R1 + R2 and deduct your first reading which should give you an approximate R2. For a ring final circuit you cannot do an r2 for the cpc as you have no end to end as such but you can use the same principle to to calculate R2 from the farthest point.
 
R2 being the CPC I don't think you should be calculating it.
There is nothing wrong with my suggestion, you are using various measurements and using some calculations to extract R2. Using a wander lead and subtracting the leads resistance is no different as this is also a calculation.
 
There is nothing wrong with my suggestion, you are using various measurements and using some calculations to extract R2. Using a wander lead and subtracting the leads resistance is no different as this is also a calculation.
You should never calculate R1 +R2. Or R2 But you can calculate your ZS. This is what the NIC have told me is acceptable
 
During the design stage it is very much acceptable to calculate R1+R2 and necessary in most of, if not all cases
I’m not talking about the design stage. I’m talking about testing on site. We should be avoiding live testing whenever possible. And doing an R1+R2 test. Then calculate the ZS. Not always possible I know but the NIC I believe are trying to get this pushed forward because people are working live on steps trying to do a ZS and having accidents
 
How do you measure R2 with no calculation. Your own method not how the NIC think it should be done.
What calculation would you need to do to perform an R2 test? You need to Null the wandering lead first if that’s what your referring to?
During the design stage it is very much acceptable to calculate R1+R2 and necessary in most of, if not all cases
also I personally think that a measured R1 +R2 test gives a more true reading than a ZS because a Zs is influenced by potential parallel paths that will lower the reading. And as we know parallel paths can be removed. If this occurred the ZS could potentially raise above the acceptable level for the circuit/ protective Device.
 
What calculation would you need to do to perform an R2 test? You need to Null the wandering lead first if that’s what your referring to?

also I personally think that a measured R1 +R2 test gives a more true reading than a ZS because a Zs is influenced by potential parallel paths that will lower the reading. And as we know parallel paths can be removed. If this occurred the ZS could potentially raise above the acceptable level for the circuit/ protective Device.
Parallel paths will in most cases result in a lower result of zs than the calculation of zs=ze+(R1+R2) rather than a higher value
 

Reply to How to test a circuits in steel conduit as the cpc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
722
Hello everyone, I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead...
Replies
1
Views
860
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
592
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
For example the house today had two lighting T&E in the same MCB. I know it's fine, but as I test both 'radials' where and how do we enter them on...
Replies
6
Views
791

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock