Discuss How to test/certify a small 230V generator installation? in the UK Electrical Forum area at ElectriciansForums.net
Hi all,
Got a client with a small barn workshop and caravan powered by a portable 230V 6kW petrol generator. (Loncin 8000D-A) . The original 32A commando lead had a domestic double skt on the end, and theres another lead with a commando socket for the caravan. Theres only one 230v o/p.
He asked me to fit 2 double skts and 2 lights so he can work in the barn, via a modern fusebox. There's also a water borehole pump.
Its not a commercial venture but temporary whilst he wants to eventually build a permanent dwelling on the site, also powered by a larger generator. Give him credit, he wants it all done proper with test certificate..
Wired that up for him with an rcd main switch db, 20A mcb for the 2 d/skts and a 6A for lights but then realised it doesnt use terra firma as an earth so cant do Zs and rcd tests, altho the rcd test button works.. Looked up the on site guide and realised it must be a floating earth type of jenny.
All dead testing is ok ..
So whats the situation with the live testing and certificate then for this temp set up?
Thanks in advance..
Well I've not seen it, so I couldn't tell you if it is or isnt.
I can tell you you shouldn't be linking N and E together without knowing for sure.
i see.. well the potential between the earth pin and each of the two brown wires measured about 90V, but an earth stake was also connected to the earth met at the db.. has this complicated things?
Whats the best test to make sure what type it is then? As you can see, I've not had any dealings with this type of scenario b4, hence my post. Thanks for yr help..
Caravan should not be used with floating earth generator, that is why you need to install a socket for it
Oh ok, thats what was happening before. Unfortunately I havent access to the gen manual but Im trying to get one online..
So it seems I may have assumed too much, see my previous reply to Rob.. so i need to establish exactly the type of earthing first then, what test to do?
As you are getting a significant voltage between each live conductor and earth, it is evidently floating at the moment, i.e. it is an IT supply. Whether it was supposed to be, by design, is another matter.
When you earth one side, making it the neutral, it becomes a TN system. Provided that there are no combined neutral-earth conductors downstream of the N-E link (there shouldn't be) it will be TN-S. It would only be TN-C if you earthed the neutral at one point e.g. on the genny, then ran a single CNE conductor to another point, where you split the earth and neutrals to the installation.
Well that is very helpful Lucien, thank you.. so it IS a TNS then if I make the link in the DB before the main switch, as suggested.
I've managed to find the manual online.. its a bit pidgin english but
it suggests (not instructs!) that the machine is grounded to an earth stake at the terminal provided, which I must admit I didn't see when I was there but I now know where to look.
You might find that the terminal is connected only to the casing, and not to either live conductor, in which case it will want to be connected to your earthing system but you will still have to make the N-E link elsewhere. Check the circuit diagram and inspect the machine to discover whether provision has been made for linking one pole or the other to earth, and that the centre-tap, if there is one, is not linked in any way.
Yes those were my thoughts too Lucien.
Beginning to get my head around this.. there doesn't appear to be any other instruction or facility on the genny to make any other link, just the connection to earth stake.
Many thanks for your help..
Reply to How to test/certify a small 230V generator installation? in the UK Electrical Forum area at ElectriciansForums.net
For emergency use, when there's a power outage, the current situation (no pun intended) is that I'm running a hook up cable from the 16A socket on...
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Hi. I am off grid, UK. There is no grid tie or connection and there is currently no potential for connection. Background: I use a Honda EU10i for...
Hi all, back again requiring some transportable building knowledge, this time round a catering/burger van and its earthing arrangment. Was asked...
10K
V
Hey guys, i have started to do some inspecting and testing, i am finding it very interesting although the certification part is a little confusing...
4K