As above, fluorescent lights have inductive ballast to regulate the current in the discharge once they light up (after the starter has pre-heated the ends and opened), so they usually have the parallel correction capacitor to compensate for that and get the overall power factor closer to unity.

I am more surprised it got in to that state without either an obvious fire or tripping breakers, etc!
 
As above, fluorescent lights have inductive ballast to regulate the current in the discharge once they light up (after the starter has pre-heated the ends and opened), so they usually have the parallel correction capacitor to compensate for that and get the overall power factor closer to unity.

I am more surprised it got in to that state without either an obvious fire or tripping breakers, etc!
Now imagine my surprise that six were in the same state, and working, with no ill effects.
 
Metallised polypropylene capacitors of this type can burn out progressively without ever taking a large enough current to trip the breaker. A transient punctures the film, the arc spreads until the film melts, but at the same time destroys the metallisation so that it's only arcing round the edges as they advance through the element. X- and Y-capacitors have a more controlled behaviour where the arc ablates the metallisation leaving the film intact,, the so-called 'self healing' process. They don't go into meltdown, but if subjected to frequent transients, gradually lose capacitance until they are inert blocks of plastic.
 

Reply to How were these still working? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
884
Had a customer message me before I went to do a job asking if I could put a new bulb in a spotlight while I was there, so I picked up some LED...
Replies
5
Views
365
Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
678
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
862
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock