orionsbelt

For this the provider has come from the pole underground to the source of the install which is a meter box outside the building in a small brick shed. Then to a 3 phase and neutral isolator , then to barn. Do i need to fit a spd or lpd devices or not? There is no lightening protection on the building
 
Yes they are now in the amendment, but what makes you think your installation is requiring them?

Have a look at 433.2.2 if it's over voltages due to atmospheric origin your concerned about

This is troubling me. I'm no expert but IMHO the "environmental conditions" in chapter 43 means the thermal conductivity of the environment where the cable runs not atmospheric conditions.
I think you should be in chapter 44 not 43.

Just my opinion.
Laurie
 
This is troubling me. I'm no expert but IMHO the "environmental conditions" in chapter 43 means the thermal conductivity of the environment where the cable runs not atmospheric conditions.
I think you should be in chapter 44 not 43.

Just my opinion.
Laurie

In the OP the poster referred to pole and overhead lines, though agreed the last leg of the supply he said was underground.

Then with the referral to SPD and lack of lightening protection, we can only assume his concerns are with over voltages of atmospheric origin and therefore my reference to section 43 and 433.2.2.

Not sure in a barn where the electromagnetic disturbances would come, unless there is equipment in it that could induce these, such as welders, fluorescent lights etc, but what would he be protecting these influences from, unless the barn is doubling up as a data centre also.
 
the passage in the regs which concerned me most is reffered to in reg 443.2 and reading this I do not think it applies . however I was firstly concerned after reading p26 0f the winter edition 2011-12 niceic connections magazine. thanks for your responces
 

Reply to I am wiring a barn conversion that is fed from an indirectly from a pole in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock