I have a job where the Ze is at 8.38 OHMS it was at 50.48 OHMS i have installed a new Earth rod but cant bring it down anymore has anyone got any advice on what I should do the mains is at least 300 meters away from the house my Zs is coming in at 8.72 OHMS for the sockets
 
if this is a TT supply then that would seem quite a reasonable figure to me, the front end time delay Residual Current Device (R C D) and hopefully the 30ma circuit protection will protect up to 200 ohms (over this is considered unstable)
 
if this is a TT supply then that would seem quite a reasonable figure to me, the front end time delay Residual Current Device (R C D) and hopefully the 30ma circuit protection will protect up to 200 ohms (over this is considered unstable)
I'm gonna go back and disconnect the main earth and turn it into a TT system as its currently a TNC-S its all protected by RCD/RCBOS
 
I'm gonna go back and disconnect the main earth and turn it into a TT system as its currently a TNC-S its all protected by RCD/RCBOS
Are you sure it is a legit TNCS ? is it an old cable with a lead sheath or could be a previous bootleg botched DIY attempt at a PME
 

Reply to I have a job where the Ze is at 8.38 OHMS in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
990
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock