how do you carry out a live/live test on i.r have done L/N,N/E and L/N all reading greater than 500

cheers
 
Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
G

Guest123

  • Thread Starter Thread Starter
  • #2
A line/line test is only carried out on a 3phase installation where obviously you have 3 line conductors and is tested at 1000V.
 

old dog

-
Arms
i think what you mean is where it states live/live on the certificate
neutral is a live conductor so live/ live = line neutral
 
P

Peter Woodford

  • Thread Starter Thread Starter
  • #4
i think what you mean is where it states live/live on the certificate
neutral is a live conductor so live/ live = line neutral

do i still need to put the results for l/n in the l/l table then

thanks
 
G

Guest123

  • Thread Starter Thread Starter
  • #5
Hi.

No the line - neutral results only go in the line neutral box. The line - line box is for measurements between phases only.

Terminology is key here, there are four colums for I/R on a full EIC, line - line, line - neutral, line - earth, and neutral - earth.

Nowhere is there a colum for live - neutral or live earth. as old dog has said the live conductors are line and neutral

Hope this helps.
 

old dog

-
Arms
do i still need to put the results for l/n in the l/l table then

thanks
sorry peter you have lost me a bit
on the schedule of test result you have insulation resistance.
under that you have a box live/live on single phase that would be line + neutral
on 3 phase that would be between lines + lines + neutral
i hope i am making this clear
what do you have on your paper work if it differs from this
ps
and the box live/ earth
 
Last edited:
P

Peter Woodford

  • Thread Starter Thread Starter
  • #7
sorry peter you have lost me a bit
on the schedule of test result you have insulation resistance.
under that you have a box live/live on single phase that would be line + neutral
on 3 phase that would be between lines + lines + neutral
i hope i am making this clear
what do you have on your paper work if it differs from this
ps
and the box live/ earth

I have live/live and live and earth so I put the live and neutral result in here is this right single phase
 

old dog

-
Arms
I have live/live and live and earth so I put the live and neutral result in here is this right single phase
yes mate live/live box line + neutral
live/earth box line +earth
thats it
but for the tests you test as gn3 page 39

why cant they leave things alone live then phase now phase is line if i just keep in mind phase/live/ is line
live can be line or neutral i think i need a cup of tea or coff no no tea
 
Last edited:

old dog

-
Arms
gn3 page 39 ? lost me
guidance note 3 page 39 has the proceedure for insulation test
testing with L+N together to earth ect dont want to confuse the post
now we have it sorted but if you have gn3 have a look i am to tiered
i need my cup of tea

so you are ok now with what goes in what box yes ?
 