Discuss i r testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A line/line test is only carried out on a 3phase installation where obviously you have 3 line conductors and is tested at 1000V.
Hi.
No the line - neutral results only go in the line neutral box. The line - line box is for measurements between phases only.
Terminology is key here, there are four colums for I/R on a full EIC, line - line, line - neutral, line - earth, and neutral - earth.
Nowhere is there a colum for live - neutral or live earth. as old dog has said the live conductors are line and neutral
Hope this helps.
do i still need to put the results for l/n in the l/l table then
thanks
sorry peter you have lost me a bit
on the schedule of test result you have insulation resistance.
under that you have a box live/live on single phase that would be line + neutral
on 3 phase that would be between lines + lines + neutral
i hope i am making this clear
what do you have on your paper work if it differs from this
ps
and the box live/ earth
ps
I have live/live and live and earth so I put the live and neutral result in here is this right single phase
yes mate live/live box line + neutral
live/earth box line +earth
thats it
but for the tests you test as gn3 page 39
why cant they leave things alone live then phase now phase is line if i just keep in mind phase/live/ is line
live can be line or neutral i think i need a cup of tea or coff no no tea
Reply to i r testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in...
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...