Discuss I replaced the light and now my heater switch won't switch on. in the UK Electrical Forum area at ElectriciansForums.net

Please explain how a spur off a 32a ring circuit is permitted then? It is permitted because the requirements for fault protection are met and overload protection is afforded by the fact that the load is restricted to 2x13a fused loads, =26a maximum. Same applies to the OP's circuit except overload protection is afforded by one, not two 13a fuses =13a.
Reading through this topic again, I do see where you are coming from.
Do you agree with my understanding being, if the OP created a fused spur, at the origin of the circuit in this case, i.e. spurred at the 32A MCB, then the 1.5 T/E is acceptable and in line with OSG H2.3. However if he had removed the ring final conductors from the MCB, the cable and FCU in question is no longer a fused spur on an RFC, and is now a radial circuit, either requiring a 20A CPD, alternatively be wired in 4.0mm T/E, as per Table H2.1
Happy to stand corrected, if I have misunderstood.
 
Thanks for your measured reply. I do not have the BBB to hand for the reg no's but overload protection to any circuit can be omitted if the load is fixed, or if the load is restricted by a downstream device. So if the OP's circuit is a radial serving a single 13a fcu then it will comply on a 32a OCPD as long as fault protection is afforded, which it almost certainly will be. That said same as you, I'd put it on a 16a device, but the advise given to the OP that putting it on a 32a is a safety issue and incorrect is wrong. It would comply.
I'm afraid your comment that a spur from the MCB is a fused spur is incorrect, it's an unfused spur. A fused spur is an extension to a ring circuit spur fed through a 13a fcu, it can serve any number of points on the load side of the fcu
 

Reply to I replaced the light and now my heater switch won't switch on. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Double wall socket switch won't switch off. It just flips back to on. The left side one is fine. It used to do this 3 years ago then was working...
Replies
1
Views
407
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
821
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
450
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
607

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock