I am instaling a night storage heater

Ib=14.78A

It=20.5A

The cable installed is a 2.5mm Flat 70' Thermoplaastic

It is installed as per method 60 Table 4A2 Which points to referance method B

Table 4D5 Does not have referance method B only A,C,100-103 Is referance method B not an accepted method of installing twin and earth?

Probably being a bit sily here:confused:
 
Last edited by a moderator:
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
Advertisement - Content continues below
S

spark1

  • Thread Starter Thread Starter
  • #2
Wotsit ,for reference method 60 you need to refer to table4D2A not table 4A2