Hello does anyone use the iCertifi software
When I enter the type of mcb for example
Type b 60898 32a it automatically comes up with 1.40 Max ZS I know it only slightly out but if bs7671 says its 1.37 that’s what it is
And you can’t manually change it .
I’ve got a assessment soon and don’t want something like this to cause a problem
 
Advertisement - Content continues below
T

The Ghost

Think you can set parameters in setting. Failing that then contact them they are brillo at getting back to you and solving problems.
 

Loki

-
Trainee
Supporter
Advent Win
I messaged them about it saying to them its because they are only going to 1 decimal place so it rounds up from 1.37 to 1.4
Got a fob off reply, I'll be going elsewhere when my subscription ends.
 
  • Thread Starter Thread Starter
  • #4
It does seem strange that it’s not giving you the correct range , I don’t think I will be sticking with it
 
Test Meter - Forum Sponsors since 2007!
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to ICertifi software problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom