Discuss If all circuits are rcd or rcbo protected max current 150mA why do you still have to install 16mm earth in the UK Electrical Forum area at ElectriciansForums.net
MCB will give overload fault protection earth leakage fault protection is provided by an RCD what other faults are there?Already answered this one in another thread.
RCD is additional protection, Above and beyond fault protection.
All circuits should be designed with fault protection in mind.
The RCD is there as an after thought.
Short circuit.MCB will give overload fault protection earth leakage fault protection is provided by an RCD what other faults are there?
No idea, think th system is bork d, click the H LP Populate Electrical News Please link and I get a permission error so it wouldn't suprise of its messed uWhy is this in the electrical news?
They fail open circuit in my experience.As others have said; an RCD is not designed Bethe primary source of protection, simply because it requires mechanical operation to work and, like any electrical components, can fail - Simple science however does not, and this is where our friends the equations come in.
Not always. They can be in service for years and keep circuits energised. Only when tested do you hear, blimey that's lucky !! Wonder how long that's been like that ??They fail open circuit in my experience.
Tell that to the people who write the OSG.Already answered this one in another thread.
RCD is additional protection, Above and beyond fault protection.
All circuits should be designed with fault protection in mind.
The RCD is there as an after thought.
The people who write the OSG are all part of one big happy family. Masters of the Universe. All gathered around a big round table.Tell that to the people who write the OSG.
Open PEN fault and you have bonding to both gas and to water which are metal and complete the neutral return for your own, if not a few, properties.How about an example of where a fault current would exist of sufficient magnitude AND TIME to justify a 16mm main earth.
So nothing to do with fault current. We are talking about a bad design which allows LOAD current to bypass all over current devices a way thats completely out of the control of the consumers side of the installation. A bit like a 5 amp rewirable fuse getting warm due to excessive load so the answer is put a 20 amp fuse wire in. Over simplistic analogy I grant you. But hope you guys can see where I have guided this one. You have answered the question put by the op which is exactly correct. Nothing to do with fault currents all to do with load currents created by bad design DNO side and BS 7671 puts its finger in the dam. Sorry for the rant but it annoys me the way these knee jerk reactions are given credibility, and its the sparky in the field left holding the Hot potato.Open PEN fault and you have bonding to both gas and to water which are metal and complete the neutral return for your own, if not a few, properties.
Currents to many tens of amps, duration as long as it takes for the DNO to find out and act.