Hello all

Ive installed a New Ring Final Circuit and have done some tests on it..

I want to learn as much as possible.

My multifunction tester does need calibrating, and sometimes i think im getting dodgy readings.. i need to spend alot more time on my tester to get familiar with it

Are my results acceptable ?




New Installed Ring Final Circuit



R1 = 0.38
R2 = 0.69
RN = 0.38



N1 – P2 = 0.90
N1 – P2 + P2 – N1 = 0.22

P + N Readings At Sockets

1. 0.22
2. 0.22
3. 0.23
4. 0.24
5. 0.22
6. 0.32 (Spur)
7. 0.26
8. 0.24
9. 0.23



CPC1 – P2 = 1.20
CPC2 – P1 + CPC1 – P2 = 0.28

P + CPC Reading At Sockets

1. 0.34
2. 0.34
3. 0.32
4. 0.30
5. 0.29
6. 0.40 (Spur)
7. 0.33
8. 0.32
9. 0.31


Insulation Resistance

N – P = >1000
N – CPC = 724
P – CPC = 673

Im baffled as to why im not getting > (greater than) on all readings?
All connections ar tight and fine..
 
hi just got home had a quick check the readings look ok for a ring aroud 50 meters in lenth
but there is something a miss on the ir readings for a new ring
 
it could be pinched cable but unlikely for both p and n to be low ir, not unheard of tho, split the ring at mid point and test both legs, if one leg shows low ir's then continue to split and test to pinpoint the part of leg with low reading. something silly will be causing this.grommets used in back boxes i assume, the readings arent very low, must be damaged /pinched cable some where, could be individual pinched conductors. again unlikely. but stuff happens.
 

Reply to I'm New to testing, Are my results ok? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

S
I seem to have located a radial circuit in the loft conversion. The Circuit is the Ring circuit from the Middle Floor which supplies only 4...
Replies
11
Views
2K
F
Hi i was looking at this old post and saw a calculation resolved which im not too sure is right and would apprciate confirmation wether it is or...
Replies
3
Views
1K
Flakey
F
T
Practicing again... TN-CS Supply New Built Home Tested ring final circuit.. P - 0.34 N - 0.34 CPC - 0.59...
Replies
24
Views
3K
spark1
S
Hello All, After posting about a CU change and the one light circuit that kept on tripping the RCD on the new CU i had a lot of great advice...
Replies
9
Views
1K
ezzzekiel
E
T
Practicing my testing and tested my first TT supply today.. It is an old farm house in the middle of no where. I know that there is things...
Replies
17
Views
4K
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock