Hi, I've been asked to go look at an immersion heater which isn't working.
I haven't looked at one before and would appreciate a heads up.
Obviously there may be a problem with the power supply or the unit may be faulty.
Would appreciate any comments by those with experience as to a suitable approach to the problem.
Cheers, Kevin
As above most likely is the element so test for supply to element first and if thats ok test element hopefully problem solved.
Chris
Check for supply at element, bypassing the thermostat if necessary. If supply there = faulty element
Very common for some of the older types of immersion to trip RCBO's straight out e.g. when 17th Ed CU fitted (had 10 out of 40 OAP flats do this on a single job!).
Chris
Hi, thanks for the reply, just a quickie, best way to test element and expected readings if faulty or not.
Also, how easy is it to remove and replace the element if it is faulty? Do I need to do anything like drain the tank etc?
Cheers Kevin
get a spark to test it you will ned to isolate it and drain tank then put new one in if found faulty but a spark will be best placed to test it for you
Don't make the mistake of fully draining the tank; just drain enough so that when you unscrew the element you dont warp the tank (expensive mistake)
Test the element line to neutral on continuity and you should read resistance of roughly
3,000 W / 230V = 13.04A
230V / 13.04A = 17.64 Ohms
Hope that helps.
If the element is shot it may be open cicuit
Yes new heaters had to be installed (by someone else subsequently so don't know how fault actually manifested itself). I'm sure I heard somewhere in a previous life that you should never megger those elements anyway.. presumably as you'd be shoving x2 or x4 it's normal operating current through a low resistance?
Don't start draining anything until you've proved the thermostat as it's very easy to check that so daft not to prove that as first step. If it's awkward to get at or to see what you're doing just kill power, disconnect the stat and pull it right out. You don't have to drain anything to go that far as the stat rod is covered within the heater assembly. Then it's simply a switch operated by a dial. Any suspicion against the stat just join the 2 wires into it to short it out, then switch on and watch whether the electric meter wheel starts whizzing round or not!
Thank you, very useful to hear a commonsense approach to problem solving, it's very easy to miss out the logical first steps (Is it plugged in?) and dive straight into the complexities.
Reply to Immersion heater faulty in the Australia area at ElectriciansForums.net
Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
4K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
4K