• IMPORTANT: The thread you're reading / posting in, could be in a DIY electrical advice area. Please be aware of your local laws. You're not allowed to provide advice to, or seek advice from, DIYers and fellow professionals in some States, Countries, Countys etc with regards to some types of electrical installations or repairs. Keep that in mind. If it's against the law where you are - always get a professional electrician in to carry out the works instead of doing it yourself. The forum will not be held responsible for any outcome of any applications of any advice sought from it.
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members

Discuss Immersion Heater Wire Changing Colour in the DIY Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:  American Electrical Advice Forum

Hi,
I need some advice please.
Last year I bought some grey H05BN4-F cable for my immersion heater.
It is 24"/61cm from my wall switch to the timer and 29"/74cm to a toolless Junction Box rated 24A. This connects to the immersion heater wire, I can't change this wire. The heater and wire look like the original ones that came with the house when it was built, 1966-1967.

The problem I have is the grey wire is changing colour, it's looking beige in different sections.

I take it the cable is failing :-/

IMG_20190527_182851.jpg

IMG_20190527_182916.jpg
 
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members

GBDamo

-
Supporter
Hi,
I need some advice please.
Last year I bought some grey H05BN4-F cable for my immersion heater.
It is 24"/61cm from my wall switch to the timer and 29"/74cm to a toolless Junction Box rated 24A. This connects to the immersion heater wire, I can't change this wire. The heater and wire look like the original ones that came with the house when it was built, 1966-1967.

The problem I have is the grey wire is changing colour, it's looking beige in different sections.

I take it the cable is failing :-/

View attachment 49594

View attachment 49595
Unless its in direct sunlight its probably heat related.

Cold be a loose connection, incorrect size coductors or, believe it or not, fake cable.

What size are the cores in the cable?

I use 3093Y 1.5mm or 2.5mm depending.
 
  • Thread Starter Thread Starter
  • #3
I thought about fake cable, as I bought it from ebay. Plus if you look up the code and find the specs, they say the insulation colour is white or black. Not grey.
I'll go to screwfix and get 3093Y 2.5mm to be on the save side.
Thanks :)
 

GBDamo

-
Supporter
I thought about fake cable, as I bought it from ebay. Plus if you look up the code and find the specs, they say the insulation colour is white or black. Not grey.
I'll go to screwfix and get 3093Y 2.5mm to be on the save side.
Thanks :)
You've managed this once without killing yourself so I'll not insult your intelligence by saying make sure your safely isolated, although I kind of just did.

Just make sure you use bootlace ferrules on the cables ends.

Quite a common failure is burnt out terminals and cables due to stranded cables splaying and giving poor connections=risistance=heat.
 

ruston

-
Mentor
Arms
Esteemed
Advent Win
Also check the old wiring , 50 + years on an immersion heater is a long time . Check the connections of the stat at the top of your tank , it is a weak spot for high resistance . Also ; as said check all your control connections .
 

suffolkspark

-
Arms
Esteemed
Heck not seen that before, 1.5mm heat flex or butyl flex will see you fine, just go and grab it from an electrical wholesaler, as above ensure you use ferrules on screw terminals or tin the ends
 

ruston

-
Mentor
Arms
Esteemed
Advent Win
Heck not seen that before, 1.5mm heat flex or butyl flex will see you fine, just go and grab it from an electrical wholesaler, as above ensure you use ferrules on screw terminals or tin the ends
Yes , Butyl is a good as you will get. The heat resistant stuff most wholesalers sell now doesn't.
 

Charlie_

-
Arms
I asked for butyl at the wholesalers on Friday, lad didn’t know what I was talking about.. He’s still learning though.
So many different terms for all sorts of products
 

Wilko

-
Arms
Esteemed
Hi - my bet is the discoloured cable has 1mm conductors. Not man enough for the job really.

If you use the immersion as your main heating for HW and it’s very old you might want to get the whole thing upgraded to include the extra thermal cutout and replace the cable end to end.
 

davesparks

-
Mentor
Arms
Esteemed
I've seen that before with cheap white rubber cable, we had a drum of it when I was an apprentice and the cable went like that whilst still on the drum.
No idea why it happened, we just chucked it in a skip.
 
Never say never but it shouldn't do. The plasticiser used in cables years ago to make them more flexible was replaced by urethane based products which doesn't as far as we know migrate from the pvc like the old plasticiser products did when in close proximity to certain materials.
 

Charlie_

-
Arms
Took some older rb cable out recently which had been ran behind insulated board, it had migrated quite badly.
 
Rubber cables deteriorate due to age from exposure to sunlight and temperature increases. Unlike pvc no chemical migration takes place it just ages as the oils dry from the rubber material a process encouraged by sunlight and temperature increases.
 
B

Bobster

Never say never but it shouldn't do. The plasticiser used in cables years ago to make them more flexible was replaced by urethane based products which doesn't as far as we know migrate from the pvc like the old plasticiser products did when in close proximity to certain materials.
Green goo!
 