- Reaction score
- 5,578
I have just fitted a new consumer unit into a house which previously just had a fuse box BS3036 with no RCD protection.
Whilst doing the testing the Zs readings were not as expected. They are around 1Ω throughout the house but at one socket they are 3.7Ω. The customer states this was the socket that was used to extend the ring into the new conservatory. The Zs readings rise further in the conservatory until they reach 4.4Ω at the far end. There are 4 sockets in the conservatory.
I shall be returning next week to investigate but as this is not something I have come across before I thought I would offer my suggestions and see if I had covered everything.
1. Check socket that tests as 3.7Ω and see if they have indeed extended the ring or just made a radial from it. Even if they had made a radial this doesn't explain the high figure at this socket but it would explain the increasing results as you go further into the conservatory.
2. Check same socket for loose connections, screw going into insulation etc which may explain higher Zs at this socket?
Any other ideas so I am prepared?