Morning all.
I'm in search of ideas.
Been installing an induction hob on a 6mm radial backed up by a 32a mcb. Came to power up yesterday and with all hobs on its throwing out the 30mA main switch rcd. (It's a TT system). Iv tested all my cables and there all clear so it's taking it out on earth leakage. I'm thinking there may be a few other items in the house with leakage and this is just taking it over the threshold. I have done a ramp test etc on the rcd and its fine.
The way I see it I can either put everything on rcbos and pop a main switch in or 100mA time delayed. Or split load DB with 2 30mA rcds and separate the circuits. But they are both expensive options. Any ideas guys??
Or I suppose leave the earth disconnected ;) JOKE!!
 
Does it trip straight away? Have you tried switching everything off at the board and leaving hob on to see if its leakage or do you have a leakage meter?
 
No it's not tripping straight away. Only when I have 2+ hobs on. Nah only got a standard clamp meter and don't do mA. I'm off back in a bit because they've had the hob exchanged as they thought it was faulty so il try just leaving it on. If it is leakage that's not due to a fault how can I get round it without sounding like I just want more money and doing the options I said above.
Thanks
 
Split the tails and put a seperate rcd in for the hob, should'nt cost much, better confirm it is leakage first though, what was the main rcd tripping at?
 
Yeh there always under like. But I don't fancy changing the rcd for one that could possibly be tripping at 27 for the extra 6mA and encounter the same problem. Il go back try this new hob. Try it on its own. If needs be pop in an rcd in an enclosure as you said
 
Have you considered the radical approach of ringing or emailing the tech support department of the appliance manufacturer and asking them whether this is normal, and if so what they recommend as a solution?

Their response my provide useful ammunition for you explaining to the client why you're charging them for installation of a new 11kV sub-station.
 
Yeah contacted ikea where it was purchased and its made by another firm and there not open during the weekends and I'm working away the next two weeks.
 

Reply to Induction hob tripping 30mA rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
780
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
768
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
312
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock