Hi all,

Probs a simple one here but when testing a 3 phase board for ze as part of a periodic inspection plus part initial verification of a small db supplied by this board should I note the main 3 phase ze within the supply parameters section of cert and then the small db as zdb within the schedule of tests? Or just use the main ze for both?

Studying for 2391-52 course

Cheers
 
Most recent NIC test sheets have it so your earth loop test carried out at the origin of supply would be your Ze. Earth loop carried out at the main switch in any fuse boards would be your Zdb

Zs would be your earth loop tests at end of circuits
 
Ze is the external loop impedance, so by definition it does not incorporate any part of the installation and can only apply at the origin.
 
Worth noting if you were completing an EICR on both these boards there would be a separate test sheet for each board and each sheet would have the supply characteristics at the top for you to fill in. so if you view it like that it will become more obvious. hope that helps.
 

Reply to Inspect and Test Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
634
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
388
Not really a Question but its more a Point that the other Education Bodies out there than City and Guilds Granted most Employment agency dont...
Replies
3
Views
739

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock