Discuss Inspection and Testing Exercise in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
29
Allright ppl,

I've bought this book and have stumbled working on exercise 2 p174 (if anyone has the book). In particular the completion of the test results for the given circuit, which is a 63m ground floor socket circuit consisting of 8 socklet outlets wired in 2.5/1.5 pvc twin and earth. 2.5 resistance is 7.41m and 1.5 resistance is 12.10m, giving total resistance of 19.51 per metre.

So
r1 = 63 * 7.41 / 1000 = 0.46
r2 = 63 * 12.10 /1000 = 0.76
rn = 63 * 7.41 / 1000 = 0.46

So I calculate R1 + R2 = 0.46 + 0.76 / 4 = 0.31

But the book says its 0.08?
 
Well whatever mistake you may be making, although I can't see any problem with it, I'm making the same one because no matter which was round I do it I get the same as you.
What does the worked answer say please mate
 
Agree with Tel and Trev. Your answer is correct.

Mistake in the book I say.

What does the worked answer say please mate


I have the book and I think the OP is referring to a Schedule of Test results specimen in the answers section at the back.

It's been filled in with values r1 = 0.46, rn = 0.46 and r2 = 0.76 but an R1+R2 value of 0.08
 
Its not the Chris Kitcher book is it ?

As you will find quite a few errors which IMO keeps you on your toes as it shows you are getting a true understanding of what you are doing!
 
I think I'd email the author and ask him to justify his answer, but then again like the kids say I'm a grumpy old git:)
 
Just had a look and it is the book!

I think you will find quite a few more errors see if you can find the PFC from the info given on exercise 6 page 178 !!
 
I find it extremely annoying when working through "examples" in these books, only to find that there is no way I can get the same answers. Eventually, one has to conclude that the book is in error (or end up with underpants on ones head and pencils up ones nose).
Do these authors never proof-read their own books?
 
I wonder how many members will dust off the said book and have a look!

Mind you its most likely me that wrong and the PFC value is looking at me (Wood trees etc comes to mind) !!!
 
it does have errors, but it's still a very good book. even the bible has errors. LOL. :bucktooth:
 
Haven't they sorted out that book yet? It had these same problems in the 16th ed of it.

Do you think Chris is bothered about the errors if it is selling copies?
I was really excited about my copy a few months ago, but quickly became disappointed with the number of errors in it. I've lost faith in whether it is correct or not now. Shame really.
 
Errors in the answers or not, seems like a book full of exercises sounds like fun. Bit Like the sudoku in the paper. I might look into this book.....
 
only ever tried that sudoku once. should be renamed sodit, cause that's what i said after 3 minutes. cannot do them, same with that rubik cube, had one when they first came out. it went over next door's fence.
 

Reply to Inspection and Testing Exercise in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
P
Hi all, I've got the 2394 written tomoz. Passed the gola and practical. Just trying to do little brush up. Got this question in a book.. A ring...
Replies
38
Views
3K
Hi, This is my first post so Hello to everyone and what a great forum this is. Just reading the practical guide to Inspection, Testing and...
Replies
8
Views
1K
MarkieSparkie
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock