Hi.
I'm planning to buy single phase walder with supply current of 16A. In got unused 32A mcb in my breaker box. I want to replace it with 16A type C or D and use about 7m long 4mm cable to connect 16A interlocked socket. Socket will go on wall of garage that is part of house.
What type of breaker is right and is cable thick enough to comply with UK domestic safety regulations.
 
Hi.
I'm planning to buy single phase walder with supply current of 16A. In got unused 32A mcb in my breaker box. I want to replace it with 16A type C or D and use about 7m long 4mm cable to connect 16A interlocked socket. Socket will go on wall of garage that is part of house.
What type of breaker is right and is cable thick enough to comply with UK domestic safety regulations.

Welcome to the forum mate.
First of all, seeing that this is a new circuit then Part P will apply (Depending on what part of the UK you live)
Secondly, the electrician you should employ, so they they can do the Part P notification, installation and test cert, will be able to tell you what size cable, cable type, installation method, breaker type.... and any other info you require.
 
Where about in the UK are you?
 
his profile says Manchester. that's a small town to the south of you , spoon. wakey wakey.

Maybe I should check out profiles more.. I've stopped looking since most of the new members has their profile locked... Not sure if this is still a thing.
 

Reply to Installation for welder in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
894
I live in Thailand and my home has 240v, 3 phase power supply. I want to add an electric car charger but first want to determine what the outlet...
Replies
0
Views
643
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
817
Hi fitting a a couple loft sockets on a radial circuit. I only have 2.5mm cable and really don’t want to buy a reel 4mm2 is it ok to use on 32A...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock