Discuss Installation Reference Method in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Reaction score
1
Hi

What is the installation reference method for flat T&E cable, with capping and buried in plaster, am I correct in thinking it is method C as all the others in table F6 (page 150) in the OSG refer to insulation?

Steve
 
method C unless it's an insulated wall that they're buried in.
 
Hi

What is the installation reference method for flat T&E cable, with capping and buried in plaster, am I correct in thinking it is method C as all the others in table F6 (page 150) in the OSG refer to insulation?

Steve

Yes, Method 'C' from Table 4A2 of BS7671 page 320, reference number 58
 

Reply to Installation Reference Method in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock