Discuss Installation Reference Method in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi
What is the installation reference method for flat T&E cable, with capping and buried in plaster, am I correct in thinking it is method C as all the others in table F6 (page 150) in the OSG refer to insulation?
Steve
method C unless it's an insulated wall that they're buried in.
Hi
Steve
Yes, Method 'C' from Table 4A2 of BS7671 page 320, reference number 58