Im doing work on an American site in the U.K. and installing us socket outlets through a transformer.
Does anyone know what I should install as far as rcds go and also the Zs readings I should expect.
Also on another site the generate 100/208 60Hz. And im installing supply cables to a DB. Are there any other factors to take into consideration when working out current rating/cable size and max Zs values.

Ollie
 
Are you installing to BS7671 or the NEC?

If working to the NEC, their specs for GFCI's are rather different to ours for RCDs, not least because on a 120V circuit they can be made much more sensitive without nuisance tripping. Permissible Zs values for a given OCPD are dependent on voltage, so you may need manufacturers data if using BS devices on voltages not tabulated in BS7671.
 
Well I suppose it’s a question to be asked. I’ll have to see if I can get hold of a copy of the NEC. The installation is bs1671 but a deviation for the outlets. They’re fed through a transformer.
The 60Hz site is a different one to get my head around. It’s swa coming from a 120/208 panel going to a DB for others to connect to.
I’ll have to ask the Americans next time I’m on site.
It’s a totally new one on me so I’m having to put the homework in, especially on the certifying side of things, and the niceic just said put a deviation in.
 
Well I suppose it’s a question to be asked. I’ll have to see if I can get hold of a copy of the NEC. The installation is bs1671 but a deviation for the outlets. They’re fed through a transformer.
The 60Hz site is a different one to get my head around. It’s swa coming from a 120/208 panel going to a DB for others to connect to.
I’ll have to ask the Americans next time I’m on site.
It’s a totally new one on me so I’m having to put the homework in, especially on the certifying side of things, and the niceic just said put a deviation in.
 
When I was in work, we needed to buy lots of 110Volt sockets from MK, the wholesaler made us sign a waiver that told them we were installing the overseas and not in the UK, so you may have some problems in the future if you use US stuff, just saying, as for the NICEIC what do they know about it, probably diddly squat.
 
When I was at work, we needed to buy lots of 110Volt sockets from MK, the wholesaler made us sign a waiver that told them we were installing the overseas and not in the UK, so you may have some problems in the future if you use US stuff, just saying, as for the NICEIC what do they know about it, probably diddly squat.
It may have been to do with export tax as you see these outlets in manufacturers catalogues sockets for export only. I know the NICEIC get a bit of a bad press on here together with the other part P scams but on their technical side, they do have some knowledgeable engineers.
 
I'm sure there was a download link on here (a while ago) for the NEC I remember downloading it. Might have been Tony uploaded it???

You could always get the cable from TerryNye's mate lololol
 
It may have been to do with export tax as you see these outlets in manufacturers catalogues sockets for export only. I know the NICEIC get a bit of a bad press on here together with the other part P scams but on their technical side, they do have some knowledgeable engineers.
Nothing whatsoever to do with export taxation.
 

Reply to Installing American in Uk in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock