installing ip 65 gu10 downlighters within 2.25 meter height of zone one.

What are the hard and fast rules because my reading of section 701 does not permit 230v ip 65 downlighters yet I see it everywhere?
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

richy3333

-
Mentor
Arms
Supporter
Esteemed
Are you saying the ceiling height is less than 2.25m and/or the fitting protrudes below that point?
 

telectrix

-
Mentor
Arms
Esteemed
IP 65, 230V downlighters are permitted in zone 1.
 

Andy78

-
Mentor
Arms
Esteemed
701.55 (xi) Shows that lights are fine in zone 1 as long as IP rated in accordance with 701.512.2.
 

telectrix

-
Mentor
Arms
Esteemed
701.55 (xi) Shows that lights are fine in zone 1 as long as IP rated in accordance with 701.512.2.
with you around , why should i pay for a copy of the regs.? o_Oo_Oo_O.
 

telectrix

-
Mentor
Arms
Esteemed
i'd be bankrupt i a month.:p:p
 