im installing a 3.96kW System on a farm. The main board in the house is roughly 100 metres away from where the solar panels are going to be placed.

they will be outside in a field where decking is being put down. i have measured up a 10mm swa cable buried will be suitable as ther is only a 2.8% voltage drop due to length of cable.

can i take the cable to a small 30mA RCD protected Garage Unit (small C.U) 16A breaker as an isolator, then to the existing house C.U to a 16A breaker? and would this have to be on an RCD also?
 
Can't see the need for a garage CU outside. What not just use a rotary isolator? RCD and 16amp protection can be in the house with a second rotary isolator as well. Isolators must be able to be locked off and a MCB does not meet that.
 
"can i take the cable to a small 30mA RCD protected Garage Unit (small C.U) 16A breaker as an isolator, then to the existing house C.U to a 16A breaker? and would this have to be on an RCD also? "

this would be on the inside of the house. there would be another ac isolator beside the waterproof inverter outside.
 
If I was doing this, I'd have a lockable rotary isolator adjacent to the inverter outside, then run the cable back to the house to another lockable rotary isolator (the "main PV AC isolator"), followed by the gen meter and either a 16A RCBO in the CU, or a separate RCD then into a 16A MCB in the CU. I'm assuming you are installing the RCD due to it being a special location (agricultural premises) - section 705 of the BRB, where an RCD up to 300mA is required.

Also bear in mind that good design practice is to limit the AC volt drop to within 1% on PV systems, not the usual 3% we are used to (sommat to do with preventing the inverter throwing a wobbly).

why cant an mcb be locked in the off position?

It can, but not without use of a special tool. An isolator than can be locked in the off position (and only in the off position) by any common or garden padlock is required.
 

Reply to Installing Photovoltaic system in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
554
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock