Discuss Instrumentation in the Industrial Electricians' Talk area at ElectriciansForums.net

Eire79

-
Reaction score
9
Advise please , I'm installing a endress and hauser system to gauge level in a DI water tank and I'm having difficulty wiring it . The instrument is a ceraphant PTP31B and the monitor inside is a RIA 45 . Has anyone wired these together on a 4 -20mA as it won't work for me it shuts down after a small pressure increase and iv checked instrument on a older model of display a RIA 250 and it works fine . So I think my wiring arrangements are out . Iv 3 wires to terminate so it's positive negative and 4-20 back . Thanks.
 

Attachments

  • 20200708_131454.jpg
    79.1 KB · Views: 15
  • 20200708_131505.jpg
    38.6 KB · Views: 15
Studying the wiring connection diagrams for the sensor and meter and noting that the sensor output is 'active' I reckon the link X2 to X8 is not needed.

What is confusing is that the 4 pin sensor plug-socket has connections for 3 wire current mode (two for power and one for active 4-20mA current source output for the meter) plus one wire for active relay control - but the meter connection diagrams do not show how to connect this arrangement - only 2 wire and 4 wire.

So P? is sensor plug and X? is meter:

P1 to X1,

P3 to X2

P2 to X4

P4 is the relay output (active high wrt to P3/X2) - the RIA45 does not have a relay input so P4 remains unconnected.

The RIA45 does have two relay outputs - the two triplets of R? terminals top left at rear.

Please let me know how you get on.
 
Last edited:
Eire79: Further to my #2 above I have found the technical documentation for the PTP31 sensor. See:

https://portal.endress.com/wa001/dla/5000557/6848/000/09/TI00384PEN_1514.pdf

Reading through it seems to me one can either buy three variants of the PTP31, ie: PTP31A, PTP31B and PTP31C or one buys a PTP31 and then configures it as an A, B or C - I cannot work out which is the case.

The letters A, B and C indicate the type measurement system that the PTP31 is employed for - see page 4 of the reference. The A model is a single relay output, the B two relay outputs and the C a relay and a 4-20mA output.

Furthermore if you look at page 6 of the reference the M12 connector on the PTP31 has 4 different pin configurations. The A1 pinout is for a single relay, A2 and A2' for two relay outputs and A3 and A3' for a relay and a 4-20mA output.

Note though there is a swap over of use of M12 pins 2 and 4 between A3 and A3'.
The pinouts A2' and A3' are associated with the DESINA cable standard.

So Sir, it seems to me you need to clarify which PTP31 sensor you have, what type of outputs/measurement system it provides and how the M12 connector is configured before connecting to the meter.
 
Studying the wiring connection diagrams for the sensor and meter and noting that the sensor output is 'active' I reckon the link X2 to X8 is not needed.

What is confusing is that the 4 pin sensor plug-socket has connections for 3 wire current mode (two for power and one for active 4-20mA current source output for the meter) plus one wire for active relay control - but the meter connection diagrams do not show how to connect this arrangement - only 2 wire and 4 wire.

So P? is sensor plug and X? is meter:

P1 to X1,

P3 to X2

P2 to X4

P4 is the relay output (active high wrt to P3/X2) - the RIA45 does not have a relay input so P4 remains unconnected.

The RIA45 does have two relay outputs - the two triplets of R? terminals top left at rear.

Please let me know how you get on.
Update. After some checks and head scratching I decided to supply sensor with a external 24v supply onto pin 1+ and 3- .
I then put the 4-20 mA pin 2 into x 4 and x8 back to - 24 V then it all worked .
So the RIA does not have enough output to supply sensor and my guess is that when mA increased it dropped voltage causing failure. It must therefore be only able to supply 2 wire or 4 wire sensors.
I wouldn't mind but the supplier said the RIA would power the sensor but obviously not the PTP 31B .
Tks for the replies , sure we are always learning something new , keeps the brain active.
 

Reply to Instrumentation in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm a service engineer from Malaysia and come across a simple problem. I work with instrumentation and the problem I face with is...
Replies
0
Views
463
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K
Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K
I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K
My customer read on many forums about people suffering to solve a problem with the above Land Rover with regards to a fault code known as P1260...
Replies
5
Views
29K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock