Good evening everybody. I've often read through these forums but never had call until today to sign up and beg for some advice! Any help would be much appreciated!
I have been working on a new domestic installation. First fix was completed before christmas. Today I returned - cut my downlight holes and discovered that the builders have filled the first floor void with 200mm of thermal insulation. The question was asked beforehand and I was informed that the void was not to be filled - this has been conveniently forgotten now though. The building is now plastered and decorated.
I have worked out a way to rewire the hob circuit, oven circuit, kitchen sockets and utility sockets circuit so most of the high load circuits have been taken care of. With the clients consent the insulation has been removed from where cables are grouped on return to the consumer unit.
For the rest though I have to work on the assumption that they are reference method 103 and that at least in part they will be grouped together (passing through joists and the like). This is of particular concern with two circuits:
A first floor sockets circuit (supplying three bedrooms, 12 sockets only, no heating/installed loads) -2.5mm ring final
A ground floor sockets circuit (supplying lounge and dining room, 5 sockets, no heating/installed loads) - 2.5mm ring final
Reference method 103 - 2.5mm current carrying capacity = 13.5 amps
Derating factor for grouping- 3 cables 0.70 = 9.45 amps
Would 16a ring final circuits be acceptable/safe in this instance do you think? Do you think I could argue that 16 amps is enough capacity to supply three bedrooms?
I would be much obliged for any help/advice. Worrying myself sick over this.
I have been working on a new domestic installation. First fix was completed before christmas. Today I returned - cut my downlight holes and discovered that the builders have filled the first floor void with 200mm of thermal insulation. The question was asked beforehand and I was informed that the void was not to be filled - this has been conveniently forgotten now though. The building is now plastered and decorated.
I have worked out a way to rewire the hob circuit, oven circuit, kitchen sockets and utility sockets circuit so most of the high load circuits have been taken care of. With the clients consent the insulation has been removed from where cables are grouped on return to the consumer unit.
For the rest though I have to work on the assumption that they are reference method 103 and that at least in part they will be grouped together (passing through joists and the like). This is of particular concern with two circuits:
A first floor sockets circuit (supplying three bedrooms, 12 sockets only, no heating/installed loads) -2.5mm ring final
A ground floor sockets circuit (supplying lounge and dining room, 5 sockets, no heating/installed loads) - 2.5mm ring final
Reference method 103 - 2.5mm current carrying capacity = 13.5 amps
Derating factor for grouping- 3 cables 0.70 = 9.45 amps
Would 16a ring final circuits be acceptable/safe in this instance do you think? Do you think I could argue that 16 amps is enough capacity to supply three bedrooms?
I would be much obliged for any help/advice. Worrying myself sick over this.