Hi everybody
I Have come across this a number of times on installations with old white pvc cable, testing with a Fluke 1652. Elecsa told me that this was due to capacitance in the wire and that it was charging up during the test. Does anybody have a more detailed explanation? The readings start at around 350meg and just keep on rising.
I am wary of holding the test button down for too long in case there is VIR hidden somewhere, but the reading is still rising after a couple of seconds. What figure should I put on my paperwork if it keeps on rising? I am currently putting the initial reading as this would be worst case scenario but not sure if this is correct.
Cheers
 
I've got a fluke 1653 and it does the same.Ipress the button, it beeps, the IR reading rises, then it beeps again. The reading to take is the second beep.
 
You know a capacitor is two conductors with insulation between. Then think of T&E. ;)

Think back to ohms law ( the R=V/I part. ) as you charge the cable the current begins to fall...which in turn means the Res will begin to increase thus your creeping IR readings.
 
Last edited:
Hi and thanks for that, although I thought the material separating the plates of a capacitor is a dielectric, which is a type of insulation with dielectric polarisation properties. An ideal insulator is a material that resists the flow of current, and that is what one would hope the pvc to do in the cable. It appears that something is happening to the pvc causing it to become dielectric and this is the question I was originally asking. Could it be an early indication of the formation of diisooctyl phtalate perhaps or some other additive reaction or some other process. Just wondered if anybody knew the chemistry.
 
eerrmmmm of course that old cookie:eek:. Sorry mate. Just know the basic facts.

All insulators can breakdown at some point.
And by the way an insulator is a dielectric
 
Last edited:

Reply to Insulation readings rising in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
803
Could someone tell me if it is possible in fluke 1663/1664 to activate the option to carry out an insulation test without having the finger fixed...
Replies
4
Views
882
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
987
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock