Discuss insulation res testing? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

brs73

-
Reaction score
4
what methods do people use for testing insulation resistance on lighting circuits,when there are loads of transformers on the circuit?
 
Agreed, I always put down that Ins Res..' between L & N on lighting circuits as a limitation.
Even though you know that the readings will be OK, you'll alway get some Smart Alec saying 'did you disconnect all the fittings / remove all the lamps??'
 
Hey.

It depends what voltage you are testing at. Really you should be disconnecting all the transformers and other electronic equipment and testing at 500V - the minumum acceptable being 1Mohm but really should be greater than 200Mohm.

If you have to test at 250V, even though the minimum acceptable is 0.5Mohm, this would only be for a SELV circuit so really the minimum for this would be 1Mohm also but as I said really should be greater than 200Mohm.

Cheers
 

Reply to insulation res testing? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in...
Replies
12
Views
1K
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
778
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
Replies
2
Views
360
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
634
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock