Discuss insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
E
essexboy
hi
just done a insulation resistance test on upstairs ring and got the following results
P-N >299Mohms
P-E >299Mohms
N-E>0.26Mohms ??????
as you can see the N-E result is unacceptable can anybody shed a bit of light on what the problem could be or how to find out where the cause of the low resisatnce reading is...
thanks for your replys :confused:
thanks for your responses
the earthing system is tn-s but the test was done at the ccu end on the upstairs ring circuit only not through the meter tails .2 fused spurs feeding shower pump and tail rail were isolated there is no other vulnerable equipment on the circuit so tested between L-N ,L-E ,N-E
not sure but could it be the fused spurs are only single pole and your getting a reading through neutral earth that way, or did you physically disconnect the pumps as well?
failed socket outlet somewhere?
something somewhere still plugged in, tv amps, etc etc
hope you get it sorted matey
go to what you think would be furthest away from board and split the ring will narrow it down, prev post about single pole could be it or maybe a trapped cable etc
Divide & conquer :D
My money is on a doubled up neutral in backbox thats been nicked by plate screw.
but did you remove the cpc and neutral from the board to do test?
as a side issue you cant do that anymore
17th says insulation test between live conductors and the cpc connected to the means of earthing:confused:
cant think why, but hey, there it is its in the regs.:eek:
ok leave the cpc connected but take the neutral and phase out
go with easy fox ,divide up and find the trapped wire /nicked wire (known it to be caught in capping before now)
Hi Shakey
do you know the reg number on that one. is it just for rings or all circuits.
thanks in advance
couldn't find my regs book before. i was just reading christopher kitchers book. p57 he says disconnect neutral or cpc.
found my regs book 612.3.1 ,can't see why, whichever is easiest would seem logical.
thanks
At what voltage do you guys do insulation resistance checks at? When I get a really low reading like posted when I do them, I can't help but to think that I might have just blown up someone's television or computer accidentally. I never have, but my mind races for a few minutes, thinking like that. We check domestic wiring at the US typically at 500 volts.
I tend to unplug everything then test at 250v as this at least gives an indication of anything still plugged in thats hidden away. If the reading is ok at 250v I bang 500v round the circuit.
Hidden items I've come across in the past:
fcu + neon behind cookerhood
Floods spured off ring final with fcu's in loft space (blew a pir on security light last week when meggered circuit :()
Tv amp in loft (either off the lighting circuit or ring)
Plug in air freshner behind bed
Tube heater in toilet taken off ring to fcu
Fitted appliances in kitchen no isolator above worktop.
Oven plugged into ringfinal.
Spur from ring final out to greenhouse feeding heaters/lights
Easyfox old chap
thats exactly what i teach my students to do,
and 612.3.2 specifically allows you to do it:D
Reply to insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
OLDBOY
O
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...