I tend to unplug everything then test at 250v as this at least gives an indication of anything still plugged in thats hidden away. If the reading is ok at 250v I bang 500v round the circuit.

Hidden items I've come across in the past:....
That's what I've taken to doing as well. Since we're dealing with a phase-to-neutral voltage of 120V here in the states, I'll do my preliminary check at 50 or 100 volts; whichever scale the megger I'm using happens to have. The stuff I miss are things like chime transformers, roof exhaust fans in the attic, television amplifiers, plug-in air fresheners, dimmer switches, and switches w/neon lights.

You all might find it interesting that megger checks are not required here in the US at all, at any interval. I do them myself following water damage, fire damage, or a hard lightning strike. Seems like the only prudent way to pass or fail the installed wiring following such occurrances.
 
md you ever worked over here in the uk?
No, but I'm pretty well tuned in to the way you all do things there. Pretty much the same as here, except you use a lot of loop feed circuits, and we're not allowed to do that here. You switch pretty much everything, which really helps with your regular testing you do of the wiring, I'm sure. You all are required to do a lot of testing on certain intervals, and we have to do *zero* testing of anything here in the states. Smart electricians do, however. Sort of a "cover your butt" type of thing. I do have a copy of the 17th edition regs, just for my own reading entertainment.
 
I'm sure I can think of many other books I'd rather have for bedtime reading! But it's certainly interesting to know the differences between the two countries.
 

Reply to insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
522
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
405
OLDBOY
O
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
978

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock