Havvy

hello everyone,
i was testing today at a fairly new house built in the last 10years and i had a problem with the insulation resistance test on both up and down stairs lighting circuits. everyother test was fine on the circuits.
on the down stairs lighting circuit L/E and N/E wouldnt each greater then >299. hovering around the 150 mark.testing between L/N the tester read 0.00.
and on the upstairs circuit clear on L/E and N/E but 0.00 on the L/N
a little puzzled any help wanted.
thank you
craig
 
Last edited by a moderator:
got to be measuring a load . either that or lenny's supermarket trolley
 
have you removed all the lamps? and what about dimmers?
 
Sounds like you have left the lamps in. To do an ir test on a lighting circuit you need to remove all lamps. Or if there are flouresants you will get low readings even if the lamps are out. I am not sure what you mean about your live to neutral tests tho.
 
As telectrix has said with the addition of fans and make sure youve disconnected the neutral from the bus bar to and be care full if your testing at 500 volts and some thing is still connected ie PIR or fans with timers you may well blow them up
 
if there is any sensitive equipment that cannot be easily disconnected, then i would not IR test between L and N, but short L/N at CU and test to E.
 
the test between live and neutral test the tester read a reading of 0.00 basically no reading. no wasnt testing at 500v start on the lowest 250v. all the lamps were removed. going back tomorrow so will have the fittinf down they were metal b and q fitting. would a smoke head mess with the results??
 
anything left in across L/N, smokes, lamps, neons, dead rats,will give you naff results.
 
Any fans or outside lights.

As everyone is saying you have something that is not disconnected,maybe loft light or hidden cupboard light with the lamps in.
 
Any fans or outside lights.

As everyone is saying you have something that is not disconnected,maybe loft light or hidden cupboard light with the lamps in.
loft light is a favorite. never think about it till head scratching time. also vanity lights, under cupboard lights, shaver points, all can f up your readings
 

Reply to insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in...
Replies
12
Views
1K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
565
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
722
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
573
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
615

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock