Doing new supplies for a school new Shneider 3 phase & N MCCB panel board. 50mm 4 core SWA one end made off in the board earth fly lead from banjo to earth terminal. The other end gland made off in gland (fly lead not made off yet) 3 phases and neutral just hanging there. Done installation resistance test to earth at 500v got 10Mohms to earth on all phases run is about 50mtrs?
 
What is it connected into at the board that’s made off? Thinking you’re reading through equipment.

Either that, or the cables damaged somewhere
 
Doing new supplies for a school new Shneider 3 phase & N MCCB panel board. 50mm 4 core SWA one end made off in the board earth fly lead from banjo to earth terminal. The other end gland made off in gland (fly lead not made off yet) 3 phases and neutral just hanging there. Done installation resistance test to earth at 500v got 10Mohms to earth on all phases run is about 50mtrs?
You mean INSULATION resistance test Mate surely
 
Did you try drying the exposed surface of the insulation between the bared ends of the cores and the gland? 10MΩ could just about be caused by condensation.

I think 'vgi' should read Vigi, Schneider's trade mark for their residual current add-on actuator.
 
you're correct pete. obviously your senile dementia is less advanced than mine. :D:D:D.
 
Could be that Tel, as well as my unhealthy addiction to anything SI FY except Dr Who, because it's not real like Star Trek.
used to think dr. who was real till he reincarnated as a scarecrow. ( jon pertpouff as worzel gummidge ). now that's taking sci-fi too far.
 
used to think dr. who was real till he reincarnated as a scarecrow. ( jon pertpouff as worzel gummidge ). now that's taking sci-fi too far.
What proved it wasn't real for me was the aerodynamics of the Tardis, impossible for a shape like that to fly let alone Time Travel, ludicrous.
 

Reply to Insulation resistance test on length of SWA cable in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
1K
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you...
Replies
0
Views
430
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you should...
Replies
0
Views
481
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock