marty1234

looking for some help
when testing jobs i find it hard to do IR testing due to appliances pluged in at back off tills, counters, shelfs,sockets above celings ,cctv that icannot get in to un plug . i dont want to damage anything doing this test i do all the other test that should be carried out an fill in the paper work what do all you guys do on jobs like this :eek:
 
Surely you have to do the alternative test then. Line and Neutral connected together and the other lead connected to earth....? And agreee with the Client or at least tell him when you go through it with him......
 
Hi Marty.

Either do as Codger suggested or put it in terms and conditions for next time that 'all appliances must be unplugged and you would need access to all accessories in all circuits' to do as you please.
 
looking for some help
when testing jobs i find it hard to do IR testing due to appliances pluged in at back off tills, counters, shelfs,sockets above celings ,cctv that icannot get in to un plug . i dont want to damage anything doing this test i do all the other test that should be carried out an fill in the paper work what do all you guys do on jobs like this :eek:

well if you cant do lives to lives then just dont. The regs allows you to reduce the test voltage to 250V for this anyway, so at least you shouldnt pop anything!
 

Reply to insulation resistance test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
522
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
Replies
2
Views
360
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
Evening chaps, I've been asked to do a visual inspection, and an insulation resistance test on a fishing boat, which is working off 24v, this is...
Replies
3
Views
2K
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock