Discuss Insulation Resistance testing - again! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Kind of related to the above thread.
I am doing the 2391 practical tommorow, to speed up my testing on a rig is there a problem with doing the Insulaion testing prior to the continuity for the Periodic?
Yes, if you don't know that you have continuity of conductors how would you know that your IR test is testing all of the circuit?
Its still a periodic inspection and test but you use the EICR to make the report.
I know you need to do it in order for new installations but I don't think you need a particular order for the periodic, I was just trying to figure out if I would be penalised for trying to do the IR on the motor circuit first when I connect across the switch.
The sequence of tests is logically formatted so you find any faults before moving onto the next test. If you did IR before continuity you would have to do the IR again if you found a break in a circuit and rectified it, saves you doing things twice.
Don't confuse EIC (Electrical Installation Certificate--on first install) with EICR (Electrical Installation Condition Report--subsequent test).
Generally, the hybrid nature of the 2391 test rig would mean that you do continuity before IR. However, on a real job, where you know everything is working beforehand then you would be interested in the Zs, without disconnecting all the circuits. So its justifiable to IR test and then Zs.
Thanks for the advice. I think I will do the continuity first to be on the safe side.
Just because its all working does not mean you have continuity of protective conductor which is what you test for.
As stated earlier, done in logical sequence so we dont have to redo earlier tests if a fault is found
In most cases it does. Once you know that the MPB's are Ok then a Zs is perfectly acceptable for each circuit. (Perhaps not so with domestic installations where the Numpties roam).
I often find cpcs are cross linked to other circuit cpcs so your R1 + R2 wouldn't give you specific circuit readings, and if you did disconnect everything you would have the hassle of reconnection at each point of separation of the cpcs.
You'll be spending week on a days worth of work if you chose to undo everything just to get your R1+R2 readings.
So its often better to get a R2 reading coupled with Ze and Zs
Reply to Insulation Resistance testing - again! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...